mull -
It's too much for me to tackle all at once. i'll nibble off a couple of pieces

Originally Posted by
mull982
...Aside from a wye-start / delta-run soft starting application what are some other applications where a motor would be wired for a wye configuration for starting and running? ...
I'm not much on motor winding theory. But there are plenty of wye wound motors out there. When I was fingering the wires for a living, that is pretty much all I saw. 99% fell into 2 - 50hp, 9 lead dual voltage. I don't know what is common now.

Originally Posted by
mull982
... What happens if you wire a motor configured for one type the other way? ...
If you connect a delta wound motor as a wye, it is a lower hp motor.
If you connect a wye wound motor as a delta -- well, I've never seen one that you could do that to. All of the wye wound motors I've seen are 9 lead or 3 lead. The 9 lead are dual voltage (usually 480/240) and the 3 lead are single voltage. The 3 lead have the wye point buried in the internals. The 9 lead has 6 coils that can be connected in series, or parallel fed. One set of three windings have the wye point already made up and buried in the internals
carl