A 1200 amp main fusible switch with 1000amp fuses can be feed with 3 sets of 500 kcmil correct?
T triplex15 Member Location Virginia Aug 5, 2008 #1 A 1200 amp main fusible switch with 1000amp fuses can be feed with 3 sets of 500 kcmil correct?
charlie b Moderator Staff member Location Lockport, IL Occupation Retired Electrical Engineer Aug 5, 2008 #2 Correct. 380 amps per conductor, times three, is 1140 amps. Welcome to the forum.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Aug 5, 2008 #3 triplex15 said: A 1200 amp main fusible switch with 1000amp fuses can be feed with 3 sets of 500 kcmil correct? Click to expand... Single or separate conduits? Yes, welcome. Where in Va?
triplex15 said: A 1200 amp main fusible switch with 1000amp fuses can be feed with 3 sets of 500 kcmil correct? Click to expand... Single or separate conduits? Yes, welcome. Where in Va?
T triplex15 Member Location Virginia Aug 6, 2008 #5 Chantilly VA and they will be in seperate conduits. Thanks