    5 ton AC
    What are the electrical specs on a 5 ton AC?
    Is there a table in the N.E.C that might help me convert to Amps, and explain d:confused, disconnect sizing, breaker sizing, conductor sizing, fuse sizing etc? :confused:
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by juz73
    No, but there are some members here that have ways of getting close enough for estimates.
    As far as disconnect sizing, breaker sizing, conductor sizing, fuse sizing etc you will have to see the units specifications or label, no way around that.
  3. #3
    Join Date
    Aug 2006
    Cape Cod, Massachusetts
    Posts
    632
    Lable on the unit usually gives you what you need
  4. #4
    5 ton AC
    Some people say ,convert to BTUH ,then to KW then divide by COP which may be 2 to 3 (to be obtained from manufacturer). The result will give you rough estimation of Elect power consumed. But I am not sure. See if someone can confirm this guideline.
    gk
  5. #5
    Join Date
    Feb 2003
    Huntsville Alabama
    Posts
    2,139
    8900 va roughly
    Some people are like slinkies. They serve absolutely no useful purpose. But still put a smile on your face when pushed down a flight of stairs.
  6. #6
    Join Date
    Dec 2005
    The Sooner Nation
    Posts
    2,437
    Rule of thumb for single phase is 10 amps per ton. For an example of a 4 ton calculation, click here.
    As the others have said, the name plate tells you what you need to know. Install your wire sized for the minimum amps and your OCP for the maximum amps.
    My son is one of the Few, the Proud, the Infidel.
    Sgt. Mickey, 0311 USMC
  7. #7
    Join Date
    Jan 2008
    Posts
    8,901
    1 Ton (air cond.) = 12,000 Btu/hr and 1 kW = 3,412 Btu/hr
    so you can get: 1 Ton (air cond.) = 12,000 Btu/hr / (1 kW / 3,412 Btu/hr) = 3.52 kW
    If you have the EER (Btu/hr-watt): kW/ton = 12 / EER
  8. #8
    Join Date
    Mar 2007
    Valdosta, GA
    Posts
    3,927
    TH's way:
    1.25 HP per ton for 1/2-5 ton capacity
    1.1 HP per ton for 5-50 ton capacity
    1.0 HP per ton for capacity above 50 tons
  9. #9
    Join Date
    Jul 2004
    Ca and Wa
    Posts
    1,507
    HP-capacity
    Quote Originally Posted by brantmacga
    TH's way:
    Does this apply to different types of compressors and their efficiencies...such as scrolled vs. piston? Just curious. rbj
    rbj, Seattle...Safety is a Professional Courtesy.
  10. #10
    Join Date
    Mar 2007
    Valdosta, GA
    Posts
    3,927
    Quote Originally Posted by gndrod
    it doesn't say. that's all the info given. I haven't used that table before; i've always been able to get the nameplate specs ahead of time. I'm sure you can e-mail tom and ask him.
Posting Permissions