code question

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
One but, the circuit can be a two wire or a multi-wire branch circuit, if it's a multi-wire branch circuit it may be shared between two legs on a single phase and center grounded delta three phase system, and either two or three phases of a wye three phase system

Roger
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I am not at all sure you really asked the question you thought you were asking. How many circuits . . . on a . . . circuit? Roger's answer is right, if he understood your question correctly. But can you clarify what you are asking for, just to be sure?

Welcome to the forum.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
I'll go with Charlie and if this is the question you are asking then a single phase would be two circuits and a three phase would be three circuits.
 
Status
Not open for further replies.
Top