Adding a new 42 circuit panel. I'm running (2) 1 1/4 emt to (2) j boxes for my receptacles Circuits. Can I use #12 thhn or 10 thhn? Would 1 1/4 emt size work?
But don't forget about the Exception to 310.15(A)(2).... Look at T.310.15(B)(3)(a) in the 2011
Good point. I was assuming a greater distance but if he is just stubbing up from the panel he may be fine.But don't forget about the Exception to 310.15(A)(2).
He'd only get a reprieve to 10% of each circuits' length (10' max.) under the exception.Good point. I was assuming a greater distance but if he is just stubbing up from the panel he may be fine.