benaround said:
Bob, So can a service rated auto/trans switch be installed up stream of an

existing service disconnect for a gen. install.

No, not really, the existing service disconnect has to disappear or become a feeder disconnect.

Any GEC running to it will have to be moved to the new service rated transfer switch. Any enclosure to neutral bonds will have to be removed. The Grounded and Grounding conductors will have to be isolated from each other.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
benaround said:
Bob, So can a service rated auto/trans switch be installed up stream of an existing service disconnect for a gen. install. Yes.
But the disconnect in a service-rated T/S is upstream of the transfer mechanism itself, so even though they share an enclosure, the disco is still upstream of the T/S.

It's a discussion of semantics, yes, but that happens a lot here. A whole lot.
 

benaround

Senior Member
Location
Arizona
iwire said:
No, not really, the existing service disconnect has to disappear or become a feeder disconnect.

Any GEC running to it will have to be moved to the new service rated transfer switch. Any enclosure to neutral bonds will have to be removed. The Grounded and Grounding conductors will have to be isolated from each other.

Exactly, that is what would have to be done. That is the answer to the question.
 
Generally, the answer is no based on NEC 230.82, but, ATS can be connected ahead of the service disconnect if the ATS is rated as service equipment and the connection/bonding of the grounded service conductors, equipment grounding conductors and grounding electrode conductors shall be remove from the existing service disconnect and move to the ATS. The existing service disconnect should be treated as feeder disconnect.
 

RUWired

Senior Member
Location
Pa.
enteng14 said:
Generally, the answer is no based on NEC 230.82, but, ATS can be connected ahead of the service disconnect if the ATS is rated as service equipment

Providing the ats has a main breaker in it.
 

360Youth

Senior Member
Location
Newport, NC
iwire said:
Actually the answer is no, transfer switches can not be installed ahead of the service disconnect. See 230.82

If you need to do that you must use a service rated transfer switch which becomes the service disconnect.

That is the best answer yet, and the only right one I can think of.

chris kennedy said:
If its service rated, it has OCP for normal power and a switch for EM power.

Actually, Generac has a new switch out that has the main service disconnect breaker but removed the genset breaker. Still SE rated.

chris kennedy said:
jrannis, is this a trick question?
OK, that is the best answer. :D
 