Jimmy7
Senior Member
- Location
- Boston, MA
- Occupation
- Electrician
Massachusetts has adopted the 2020 Code. Article 230.85 of the 2020 code requires an emergency disconnect on one and two family dwellings that should be located in an outdoor accessible location. I was just asked by a building contractor to replace and relocate a 200 amp underground meter socket. With the new location of the meter socket I wouldn't have to touch the 200 hundred amp panel, just the conductors between the meter socket and the panel. With this new code article I was planning on installing a meter main in order to abide by 230.85. My question is this, do I have to change out the main breaker panel to a main lug only panel? I know the panel will be classified as a subpanel because the service disconnecting means will be outside, so I'll have to separate the neutrals and the grounds. Could you give me your thoughts on this