old67cajun
need recommendation of nitrogen bottle and regulator to service skid transformers to re pressure nitrogen blanket. 34.5kv to550v three phase transformer, cooper material number 00022A65XXMA
Click on the persons name you want to have a private conversation with and then click "start conversation", it is not a good idea to post private email addresses in public.could I get your email to share specifics?
when i click on persons name all I get is a follow option nothing about conversation.
In my readings of railroading, I came across an article that described in detail the Milwaukee Road's electrified lines in the Pacific Northwest. In the 1930's, I think, a substation was destroyed when lightning caused arcing in a transformer that ignited gases from the cooling oil that had built up in the open spaces above the oil. After that, the open spaces in the transformers were pressurized with nitrogen.Why do transformers need an N blanket? Do all 5MVA and over have one or a bottle? Round here all the ones in my POCO's substation appear to have one.
Not all have a blanket. The blanket also helps keep out moisture with positive pressure. The tank breathes and when it cools it will draw in nitrogen rather than moist air. Tank seals will eventually leak.Why do transformers need an N blanket? Do all 5MVA and over have one or a bottle? Round here all the ones in my POCO's substation appear to have one.
Overheating and chemical breakdown are key. Usually heat is the main culprit. If you have arcing in a normal transformer then you have reached a whole other level of problems.That would make sense. Any idea if it can also take place from other reasons or just arcing? I know my POCO had a big issue with a few of its trafos gassing so much so they mentioned it in an annual report years back.
Regular oil sample tests including DGA will help you see what is going on inside. Annual samples are highly recommended and more frequent for problem or high risk units.
Simply need some quotes for pricing of a bottle and regulator ready to go. The project was suppose to start weeks ago, so time is crucial.
What is swag?2-stage 0-15 PSI regulator from McMaster-carr:
$555.19![]()
McMaster-Carr
McMaster-Carr is the complete source for your plant with over 595,000 products. 98% of products ordered ship from stock and deliver same or next day.www.mcmaster.com
McMaster-Carr isn't the cheapest option, but you can have it the next day if you want. Convenience is worth something.
Call your local Praxair branch for the cost of the nitrogen bottle, size your choice. Any welding supply store should be able to sell you a N2 cylinder. Note that you want to buy it, not rent it.
I'd probably add another ~$250 for gas lines, fittings, and other associated shmoo.
This is a SWAG, based on other pneumatics projects I've done (I've never plumbed a transformer for N2).
SceneryDriver