hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please all response NEC 2014.
Attached sketch show 4 position meter stack with terminal box one enclosure. Two meters with 200A breakers are on right and two meters with 200A breakers are on left. Sketch has following:
1. I have neutral bar #1 , equipment grounding conductor bar # 1 on right with neutral to ground bond
2. neutral bar #2, equipment grounding conductor bar #2 on left with neutral to find bond
3. neutral bar on terminal box incoming utility
4. Main grounding electrode system connection is made on the right only shown on sketch ground symbol.
The incoming utility service conductors land on neutral bar then connect to right and left neutral bars as shown.
I have two neutral to ground bond one left and one right.
Have the following questions:
1. How do you size neutral to ground bond based which incoming conductors?
2. Can you have two neutral to ground bonds as shown? Is it in compliance with NEC 2014 Section 250? I did see exception 250.24(B) NEC 2014 to have one overall but not sure if you can have two each side as shown for two meters 200A bkrs each side as shown.
Attached sketch show 4 position meter stack with terminal box one enclosure. Two meters with 200A breakers are on right and two meters with 200A breakers are on left. Sketch has following:
1. I have neutral bar #1 , equipment grounding conductor bar # 1 on right with neutral to ground bond
2. neutral bar #2, equipment grounding conductor bar #2 on left with neutral to find bond
3. neutral bar on terminal box incoming utility
4. Main grounding electrode system connection is made on the right only shown on sketch ground symbol.
The incoming utility service conductors land on neutral bar then connect to right and left neutral bars as shown.
I have two neutral to ground bond one left and one right.
Have the following questions:
1. How do you size neutral to ground bond based which incoming conductors?
2. Can you have two neutral to ground bonds as shown? Is it in compliance with NEC 2014 Section 250? I did see exception 250.24(B) NEC 2014 to have one overall but not sure if you can have two each side as shown for two meters 200A bkrs each side as shown.