Part VI. Service Equipment — Disconnecting Means
230.70 General.
Means shall be provided to disconnect all ungrounded conductors in a building or other structure from the service conductors.
230.70(A) Location.
The service disconnecting means shall be installed in accordance with
230.70(A)(1), (A)(2), and (A)(3).
230.70(A)(1) Readily Accessible Location.
The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
230.70(A)(2) Bathrooms.
Service disconnecting means shall not be installed in bathrooms.
230.70(A)(3) Remote Control.
Where a remote control device(s) is used to actuate the service disconnecting means, the service disconnecting means shall be located in accordance with
230.70(A)(1).
230.70(B) Marking.
Each service disconnect shall be permanently marked to identify it as a service disconnect.
230.70(C) Suitable for Use.
Each service disconnecting means shall be suitable for the prevailing conditions. Service equipment installed in hazardous (classified) locations shall comply with the requirements of Articles
500 through
517.
230.71 Maximum Number of Disconnects.
Each service shall have only one disconnecting means unless the requirements of
230.71(B) are met.
230.71(A) General.
For the purpose of this section, disconnecting means installed as part of listed equipment and used solely for the following shall not be considered a service disconnecting means:
- (1)
Power monitoring equipment
- (2)
Surge-protective device(s)
- (3)
Control circuit of the ground-fault protection system
- (4)
Power-operable service disconnecting means
230.71(B) Two to Six Service Disconnecting Means.
Two to six service disconnects shall be permitted for each service permitted by
230.2 or for each set of service-entrance conductors permitted by
230.40, Exception No. 1, 3, 4, or 5. The two to six service disconnecting means shall be permitted to consist of a combination of any of the following:
- (1)
Separate enclosures with a main service disconnecting means in each enclosure
- (2)
Panelboards with a main service disconnecting means in each panelboard enclosure
- (3)
Switchboard(s) where there is only one service disconnect in each separate vertical section where there are barriers separating each vertical section
- (4)
Service disconnects in switchgear or metering centers where each disconnect is located in a separate compartment
Informational Note No. 1: Metering centers are addressed in UL 67,
Standard for Panelboards.
Informational Note No. 2: Examples of separate enclosures with a main service disconnecting means in each enclosure include but are not limited to motor control centers, fused disconnects, circuit breaker enclosures, and transfer switches that are suitable for use as service equipment.
230.