rustymetal
Member
- Location
- Ohio
- Occupation
- On Site Assistant
120/208 High leg delta service
4 Wire- 208v[red A]/120v[black B]/120v[black C]/Green[service] and green[ground rod] bonded on N busbar. 1950's farm building.
I go to this service and problems.. the main breaker - not powering the C phase bus bar.
But a 240v/30A drain waste sub is back feeding into the C phase via the actual pump. The lights being powered via pump leg are quite a show.
The panel gets changed out.
During the change out I may have switched B/C phase.
After I put the meter back in the high leg is reading 320v to ground, 420v to phase B, 240 to C.
How can this be? When I pulled the meter there is clear a unacceptable level of corrosion... service conduit is not connect... fittings are just missing... The meter box is scheduled to be changed. But what did I do wrong?
How could I even change the voltage? Maybe I missed the grounding bushing? Corrosion at fault? Meter put in upside down?
4 Wire- 208v[red A]/120v[black B]/120v[black C]/Green[service] and green[ground rod] bonded on N busbar. 1950's farm building.
I go to this service and problems.. the main breaker - not powering the C phase bus bar.
But a 240v/30A drain waste sub is back feeding into the C phase via the actual pump. The lights being powered via pump leg are quite a show.
The panel gets changed out.
During the change out I may have switched B/C phase.
After I put the meter back in the high leg is reading 320v to ground, 420v to phase B, 240 to C.
How can this be? When I pulled the meter there is clear a unacceptable level of corrosion... service conduit is not connect... fittings are just missing... The meter box is scheduled to be changed. But what did I do wrong?
How could I even change the voltage? Maybe I missed the grounding bushing? Corrosion at fault? Meter put in upside down?