Gentlemen ,Why my induction motor is drawing 5.5 A current with no load , when connected in star And 60A when connected in delta ?
Yes , this motor is rated for 460V/60Hz and tested with same voltage in both star and delta as well. The currents are almost balanced. In start connection L1=5.2,L2=5.2,L3=4.9 whereas with delta it is L1=60.2,L2=60.1,L3=55.1
... My guess is that the motor is _rated_ for 460V 60Hz in the star configuration, and is not actually intended for use in the delta configuration at this voltage.
Following every one else's posts - which are all pretty good:
My
guesses are:
Synchro is right on
Jon is right on
This is a 7.5hp motor, rated for 460V,
It is not intended to be used Wye-Delta Start. Nobody wye-delta starts a 7.5hp motor.
It has to be either a 6 lead or a 12 lead, which would be uncommon for a single voltage motor
Otherwise you could not connect in delta
Unless:
It I a 9 lead motor and you tried to connect it delta. And that would not work. And the nameplate would show two voltages, 480V connection and a 240V connection.
For now, stick with: It is rated for 460V and the connection will be Wye.
I'm thinking we really need some more context here.
Question:
480V, 60HZ sounds pretty North American. Most all the time, a "Star connection" is referred to as "Wye". Which makes me think, "other than North American". Just curious, where is this located?