Transformer connections for wye wye transfromers. Connecting a 480v wye /277 to 400v wye 230v transfromer from a 3 wire 480 source.
Yeah . . . wye?I'm curious why the OP wants to use a Y primary given the technical issues that it presents.
Looks like ho and xo are commonDoes this particular wye:wye transformer have a tertiary winding? If not you may have poor line-neutral voltage regulation. I presume this is a three phase transformer with a common 3 leg core. If not, all bets are off.
See http://apps.geindustrial.com/publibrary/checkout/GET-3388B?TNR=White Papers|GET-3388B|generic
The problems of wye:wye transformers are described on the first page.
-Jon
To the op: Are you sure you have a wye:wye transformer, and not a three phase autotransformer with a wye coil arrangement?
It is a autotransfromerTo the op: Are you sure you have a wye:wye transformer, and not a three phase autotransformer with a wye coil arrangement?
Yes it is a autotransfromerTo the op: Are you sure you have a wye:wye transformer, and not a three phase autotransformer with a wye coil arrangement?
member: 163595"]
Looks like ho and xo are common
[/QUOTE]It is a autotransfromer
I believe you have the wrong transformer for the job.
Remember that if you want to supply line to neutral loads from a wye system, you are required to ground the neutral.
In addition to the problems of poor neutral voltage regulation, your transformer neutral is electrically connected to both your input and output. This means that the transformer neutral is going to try to act as a neutral for your _entire_ supply system, not just your secondary loads.
You state that you have a 480V 3 wire source. You don't state if you have an ungrounded delta, a grounded delta, or 3 wires from a grounded wye supply. If you have an ungrounded delta, then this transformer is going to try to act like a grounding transformer for the entire system. If you have a grounded delta supply, then grounding the neutral of this transformer will result in a short circuit.
If you have a grounded wye supply, then you are going to need to bring all 4 wires to this transformer to provide the correct neutral reference.