Hey everyone,
I have a project where I am providing a short circuit evaluation and there are two roof top units that each have a short circuit current rating (SCCR) of 5000 amps. The available fault current at the roof top units is about 8000 amps at both units. The roof top units obviously do not pass the evaluation, but the contractor is asking me to help him find solutions because they already ordered the units and decided to do the study after the fact... Outside of increasing the feeder lengths, would it be acceptable to put fusible disconnects a head of the equipment? The roof top units that they ordered came with non fusible disconnects, but could they just provide their own fusible disconnects ahead of these? I was reading through Trane's literature and they provided a note for what they call their "High Short Circuit Current Rating" for equipment. This note reads "Unit shall be provided with electrical subsystem that will withstand fault currents up to 65kA (208/ 230, 460 VAC) or 25kA (575 VAC) compliant with UL 1995 and NEC 440.4 (B). Each compressor circuit and the indoor fan shall have dedicated overcurrent protection. Three phase motors shall be protected by Class J time delay fuses. Single phase motors shall be protected by Class CC time delay fuses. All transformers shall also be protected with Class CC time delay fuses. Contactors shall be din rail mounted." It seems to me they are providing fusible disconnects to achieve a high SCCR anyways. Please let me know what you all think.
I have a project where I am providing a short circuit evaluation and there are two roof top units that each have a short circuit current rating (SCCR) of 5000 amps. The available fault current at the roof top units is about 8000 amps at both units. The roof top units obviously do not pass the evaluation, but the contractor is asking me to help him find solutions because they already ordered the units and decided to do the study after the fact... Outside of increasing the feeder lengths, would it be acceptable to put fusible disconnects a head of the equipment? The roof top units that they ordered came with non fusible disconnects, but could they just provide their own fusible disconnects ahead of these? I was reading through Trane's literature and they provided a note for what they call their "High Short Circuit Current Rating" for equipment. This note reads "Unit shall be provided with electrical subsystem that will withstand fault currents up to 65kA (208/ 230, 460 VAC) or 25kA (575 VAC) compliant with UL 1995 and NEC 440.4 (B). Each compressor circuit and the indoor fan shall have dedicated overcurrent protection. Three phase motors shall be protected by Class J time delay fuses. Single phase motors shall be protected by Class CC time delay fuses. All transformers shall also be protected with Class CC time delay fuses. Contactors shall be din rail mounted." It seems to me they are providing fusible disconnects to achieve a high SCCR anyways. Please let me know what you all think.