Typical, areas around diesel fuel are not considered classified because of the flash point of diesel. See 514.3(A)
It might be a div 2 area from being wastewater as opposed to diesel. It is also possible that someone just put seals in for no good reason.Thanks for reply. This is a wastewater treatment plant where NFPA 820 is observed. Any reference in there?
Some of the existing conduit in that area has seal offs and explosion proof device boxes...
It might be a div 2 area from being wastewater as opposed to diesel. It is also possible that someone just put seals in for no good reason.
Are you planning to plug that pump into the receptacle? It's possible that the pump motor is not suitable for a division 2 area.
Why a concrete containment for what appears to be a double walled tank? If it is not a double wall tank, then I don't think an automatic sump pump is permitted inside the concrete containment....
Yes, the plan was to put a receptacle for that sump pump to drain the containment area when there's a rain event.
Good question and I agree you can't put an automatic sump there if it is for containment. Maybe it is not being used to collect spills or leaks. Someone just wanted to put some physical protection around it.Why a concrete containment for what appears to be a double walled tank? If it is not a double wall tank, then I don't think an automatic sump pump is permitted inside the concrete containment.
Interesting, but it says "Where the authority having jurisdiction can satisfactorily determine that the flammable liquids having a flash point below 100F, such as gasoline, will not be handled, such location shall not be required to be classified." So perhaps this applies to the containment area of the tank.Typical, areas around diesel fuel are not considered classified because of the flash point of diesel. See 514.3(A)
the flash point of diesel exceeds 100 deg f so the sentence you quoted just does not apply.Interesting, but it says "Where the authority having jurisdiction can satisfactorily determine that the flammable liquids having a flash point below 100F, such as gasoline, will not be handled, such location shall not be required to be classified." So perhaps this applies to the containment area of the tank.
I'm assuming that if you handle it, such as pumping it, it now must be classified? I would think there would be a class I, Division 1 bubble with a three feet radius around the end of the pump spout. Anyone?
That's one.
probably cheaper to build everything the same way rather than having two versions. I can't say I have ever seen a concrete diesel tank though.The few times I have installed that type of equipment for both gas and diesel, the equipment was built exactly the same way for both products. That is all built in accordance with Figure 514.3(B).
That's two. I was able to zoom in on it after I saved the photo. There is a third clue on the photo and at least one, a bit more subtle clue, that isn't in the photo itself.I can't tell from the picture for sure but might be the switch next to the hose reel is XP. Looks like it might have a red nameplate.
If there was a pile of lumber there you could have a similar sign as lumber is also combustible.
Is combustible the same thing as flammable?If there was a pile of lumber there you could have a similar sign as lumber is also combustible.