Why doesn't type MC cable have a bonding strip? What if the middle of the run was damaged or drilled into?
Because it has an insulated green conductor as the EGC. The jacket is still bonded by the connector at each end and not designed to carry the circuit fault current but I see your point if the jacket itself was faulted by a screw or something.
My guess is that the odds of it being a problem are very slim so it's not a concern.Without the bond strip the jacket would present a high impedance path during a fault internal to the cable itself.
'Cause then it would be AC, but with a ground wire.Why doesn't type MC cable have a bonding strip? What if the middle of the run was damaged or drilled into?
My guess is that the odds of it being a problem are very slim so it's not a concern.
It should be bonded on both ends if properly terminated.
So if damaged in the middle, it would have a fault part either way.
So, basically are you saying they should ban MC? Or require the strip and have only a hybrid product?But no bonding strip to lower the Z.
Unless its for a GFCI requirement, like a drinking fountain.Write a proposal for a ban due to the infinitesimal possibility that something bad can happen. Infinitesimal with no substantiation seems to dictate what they'll approve.
So, basically are you saying they should ban MC? Or require the strip and have only a hybrid product?
exactly what BX is famous forWithout the bond strip the jacket would present a high impedance path during a fault internal to the cable itself.
exactly what BX is famous for
I will bet if the MC cable is so damaged the the EGC is severed, a bonding strip will not be much better.
Until it happens... there was a PDF of a burned up MC cable in a butcher shop.