Is there any ambiguity here though? I would have to double check the language as I don't remember the exact wording offhand, but doesn't it say "rating of the service"? Is that the ampacity of the service conductors, and what about the 83% sizing?Using a line side tap, the only NEC limit is the nominal size of the service, in this case 200A. But the POCO may have their own limits based on both the service size and the voltage stability of your specific transformer secondary and its primary feed.
Is there any ambiguity here though? I would have to double check the language as I don't remember the exact wording offhand, but doesn't it say "rating of the service"? Is that the ampacity of the service conductors, and what about the 83% sizing?
The 200 amp service starts at the meterbase or main breaker.IMO.
Anything on the line side of the meter you have to get POCO permissions and should be part of your power purchase agreement if there is one..
Back feeding on the line side is also limited by the transformer and the utility wire size. Kva is kva, regardless of which way it’s feeding.
You don’t have underground there? Some, if not most places for UG services have a demarcation point at the meter.Per the NEC, the point of demarcation is the service point, not the meter or the disconnecting means (unless they happen to be the same).
Around here that would typically that the conductors between the weatherhead and the meter/main need to meet the AHJ's idea of 200A.
You don’t have underground there? Some, if not most places for UG services have a demarcation point at the meter.
Also, a line side connection could still be at the top of the weather head.
We have lots of them on our system that are connected on line side.
So Ben what in your opinion would be the max backfeed for a 200 amp residential service that has 4/0 AL service conductors? Considering the continuous load adder I doubt there would be a problem going 160A inverter output=200A calculated, but should we keep it at 144A inverter output/180A calculated?I concur that per the NEC the max is 200A, if that is the rating of the service.
This is indeed ambiguous in my opinion. Put it this way: maybe the OP needs to settle the question of what the service is really rated. 200A would be a huge system for residential though. Hopefully this is not the controversy.
You don’t have underground there? Some, if not most places for UG services have a demarcation point at the meter.
Also, a line side connection could still be at the top of the weather head.
We have lots of them on our system that are connected on line side.
So Ben what in your opinion would be the max backfeed for a 200 amp residential service that has 4/0 AL service conductors? Considering the continuous load adder I doubt there would be a problem going 160A inverter output=200A calculated, but should we keep it at 144A inverter output/180A calculated?
My argument would be you better forget the NEC and ask the POCO.I don't have a strong opinion, and I've never had to deal with the question in the field. I've just noticed that the code has never explicitly addressed it. I suppose my initial take would be 'if it's good enough for 200A in, it's good enough for 200A out.' The counter-argument might be 'the allowance for dwellings in 310 basically assumes the current is not continuous, but inverter output would be continuous.'
FWIW, 2020 705.11 changed it from 'rating of service' to 'ampacity of service conductors'. But this just raises a new question of whether the 'ampacity' must be considered before the allowance for dwellings is included, or may be considered after.
What is the maximum amount of solar amperage backfeed allowed on a 200 amp residential service? I've heard conflicting interpretations of the code. Just curious what others are doing.
I would agree the 144 complies with the Code for 4/0 aluminum
Then hope that meter base and meter doesn't melt under the continuous load...especially if it is in direct sunlight.
My argument would be you better forget the NEC and ask the POCO.
My argument would be you better forget the NEC and ask the POCO.
I would think it would all get flushed out during the interconnect agreement process, but I guess some who dont know what they are doing would just build it then call the POCO to come hook it up