I do not understand how 16 AWG extension cords (cord sets) are considered protected by a 15 ampere or 20 ampere circuit breaker. I know this is OK, but I just don't see where the NEC (or UL 817) allows this.
---
2020 NEC 400.16 Overcurrent Protection (for Flexible Cords and Flexible Cables) says: "Flexible cords not smaller that 18 AWG, and tinsel cords or cords having equivalent characteristics of smaller size approved for use with specific appliances, shall be considered as protected against overcurrent in accordance with 240.5."
2020 NEC 240.5(B)(3) Protection of Flexible Cords, Cables and Fixture Wires / Branch Circuit Overcurrent Device / Extension Cord Sets says: "Flexible cord used in listed extension cord sets shall be considered to be protected when applied within the extension cord listing requirements."
I do see where 2020 NEC 240.5(B)(4) says "20-ampere circuits - 16 AWG and larger" but this is only for "Field Assembled Extension Cord Sets."
---
The label on such an extension cord (6 feet long) that I have says: "16 Gauge, 13 Amp, 125 Volt."
---
The applicable UL Standard is UL 817 Cord Sets and Power-Supply Cords.
UL 817 Table 114 Cord Ampacities and Voltage Ratings shows these type of cords at 13 amps up to 50 feet, and 10 amps over 50 feet.
UL 817 Table 115 Cord-Set Ratings shows for 15 amp up to 50 feet a 14 AWG would be required, more than 50 feet a 12 AWG would be required. For 20 amp up to 50 feet a 12 AWG would be required, more that 50 feet a 10 AWG would be required.
---
What am I missing?
---
2020 NEC 400.16 Overcurrent Protection (for Flexible Cords and Flexible Cables) says: "Flexible cords not smaller that 18 AWG, and tinsel cords or cords having equivalent characteristics of smaller size approved for use with specific appliances, shall be considered as protected against overcurrent in accordance with 240.5."
2020 NEC 240.5(B)(3) Protection of Flexible Cords, Cables and Fixture Wires / Branch Circuit Overcurrent Device / Extension Cord Sets says: "Flexible cord used in listed extension cord sets shall be considered to be protected when applied within the extension cord listing requirements."
I do see where 2020 NEC 240.5(B)(4) says "20-ampere circuits - 16 AWG and larger" but this is only for "Field Assembled Extension Cord Sets."
---
The label on such an extension cord (6 feet long) that I have says: "16 Gauge, 13 Amp, 125 Volt."
---
The applicable UL Standard is UL 817 Cord Sets and Power-Supply Cords.
UL 817 Table 114 Cord Ampacities and Voltage Ratings shows these type of cords at 13 amps up to 50 feet, and 10 amps over 50 feet.
UL 817 Table 115 Cord-Set Ratings shows for 15 amp up to 50 feet a 14 AWG would be required, more than 50 feet a 12 AWG would be required. For 20 amp up to 50 feet a 12 AWG would be required, more that 50 feet a 10 AWG would be required.
---
What am I missing?