I looked at a new, in progress, 120/208V 3ph 4 wire 600 amp service for a friend he is having installed at his business. The 600 amp main disconnect (breaker) has its' own enclosure. Brand is Square D.
A steel plate, (bus bar?), is used for the Line parallel neutral conductors two barrel mechanical lug and the load neutral parallel conductors 2 barrel mechanical lug. The way the guy has it wired the steel plate is a current carrying conductor. Does a steel plate meet the definition of a current carrying bus bar? Is it code? If yes where would I find it in the 2017 NEC.
I've, seen, used, copper and aluminum bus bars. I've heard of brass bus bars but I never seen or used steel for a current carrying bus bar.
Notice in the picture the guy didn't even remove the paint from the steel plate where he installed the lugs. Or does Square D use conductive paint now days?
Picture of terminations.
.
A steel plate, (bus bar?), is used for the Line parallel neutral conductors two barrel mechanical lug and the load neutral parallel conductors 2 barrel mechanical lug. The way the guy has it wired the steel plate is a current carrying conductor. Does a steel plate meet the definition of a current carrying bus bar? Is it code? If yes where would I find it in the 2017 NEC.
I've, seen, used, copper and aluminum bus bars. I've heard of brass bus bars but I never seen or used steel for a current carrying bus bar.
Notice in the picture the guy didn't even remove the paint from the steel plate where he installed the lugs. Or does Square D use conductive paint now days?
Picture of terminations.
.