Looking at the option of installing a 240V/120V 3000VA Step-Down Isolating Transformer for a project. Need some clarification on the Primary/Secondary protection rules.
I chose 3000VA because the sign needs to be fed with a 20A circuit per the 600's, although the 600's doesn't specify what the voltage rating of that circuit must be.
In my mind, I start with 120V * 20A = 2400VA. Since 2.5kVA xfrmr seems to be rather uncommon, I went with 3kVA because (1) it's more common and (2) I would not be loading the xfrmr to the near maximum capacity per its' nameplate rating, ideally increasing the longevity of the unit.
So, say I want my Secondary to be limited to 20A @ 120V or 2400VA...
If I do *Primary Protection ONLY*...
For the Primary OCPD, that's 2400VA/240V = 10A. That's greater than 9A, so per Table 450.3(B), Max OCPD = 10A x 1.25 = 12.5A (next size up yields 15A OCPD).
However, and I know this is rather theoretical and OCPD tolerances are different, but say the circuit, for whatever reason, pulls 14.99A, not tripping that OCPD.
That's 14.99A x 240V = ~3600VA, which is greater than the transformer VA rating. How is this allowed if theoretically the circuit could pull more power than the xfrmr is rated for? Am I doing something wrong? Can most transformers handle MORE than their nameplate rating??
If I do BOTH *Primary AND Secondary Protection*...
For the Secondary OCPD, that's 2400VA/120V = 20A. That's greater than 9A, so per Table 450.3(B), Max OCPD = 20A x 1.25 = 25A (25A is considered a standard size per 240.6, even though I kind of chuckle at this notion).
Again, utilizing the same logic as above, that's 25A x 120V = 3000VA (maxed, but safe). This would also prevent the primary circuit from exceeding 12.5A, which eliminates the Primary protection problem of exceeding the xfrmr VA rating.
It seems to me, the best solution is to do BOTH Primary and Secondary protection....
I chose 3000VA because the sign needs to be fed with a 20A circuit per the 600's, although the 600's doesn't specify what the voltage rating of that circuit must be.
In my mind, I start with 120V * 20A = 2400VA. Since 2.5kVA xfrmr seems to be rather uncommon, I went with 3kVA because (1) it's more common and (2) I would not be loading the xfrmr to the near maximum capacity per its' nameplate rating, ideally increasing the longevity of the unit.
So, say I want my Secondary to be limited to 20A @ 120V or 2400VA...
If I do *Primary Protection ONLY*...
For the Primary OCPD, that's 2400VA/240V = 10A. That's greater than 9A, so per Table 450.3(B), Max OCPD = 10A x 1.25 = 12.5A (next size up yields 15A OCPD).
However, and I know this is rather theoretical and OCPD tolerances are different, but say the circuit, for whatever reason, pulls 14.99A, not tripping that OCPD.
That's 14.99A x 240V = ~3600VA, which is greater than the transformer VA rating. How is this allowed if theoretically the circuit could pull more power than the xfrmr is rated for? Am I doing something wrong? Can most transformers handle MORE than their nameplate rating??
If I do BOTH *Primary AND Secondary Protection*...
For the Secondary OCPD, that's 2400VA/120V = 20A. That's greater than 9A, so per Table 450.3(B), Max OCPD = 20A x 1.25 = 25A (25A is considered a standard size per 240.6, even though I kind of chuckle at this notion).
Again, utilizing the same logic as above, that's 25A x 120V = 3000VA (maxed, but safe). This would also prevent the primary circuit from exceeding 12.5A, which eliminates the Primary protection problem of exceeding the xfrmr VA rating.
It seems to me, the best solution is to do BOTH Primary and Secondary protection....