Perhaps a dumb question...
Thinking about installing a 240V/120V Step-Down Isolation Transformer (i.e. SDS).
As it stands, the plan is to transfer from an underground Sch. 80 1/2" PVC to 1/2" IMC (not the part I want you to critique, haha) and land that on the input/primary side of of the SDS. Because of the PVC run, my initial thought is to pull a wire type EGC from the building metal conduit system/last interior j-box to the SDS outside and bond it to the enclosure... so that in the case of a primary side fault at the SDS, the primary OCPD can trip.
On the output/secondary side (i.e. same enclosure) will be an IMC threaded nipple to (1) 60A 2 Position Outdoor Load Center. Per "some NEC Code I don't feel like looking up right now," the (1) SBJ, (2) SSBJ, (3) GEC, and (4) EGCs for the SDS will terminate in this enclosure (i.e. the first disconnecting means of the secondary).
My question is... is there any potential for a ground loop here because I will have BOTH (1) a wire type EGC coming from the building to the SDS enclosure... and (2) a metal conduit bonding the SDS to the first disconnect, which will be grounded to a new ground rod.
I can't but wonder if I should avoid the EGC coming to the SDS from the building... and just let it be grounded at the first disconnect.
Thoughts?
Thinking about installing a 240V/120V Step-Down Isolation Transformer (i.e. SDS).
As it stands, the plan is to transfer from an underground Sch. 80 1/2" PVC to 1/2" IMC (not the part I want you to critique, haha) and land that on the input/primary side of of the SDS. Because of the PVC run, my initial thought is to pull a wire type EGC from the building metal conduit system/last interior j-box to the SDS outside and bond it to the enclosure... so that in the case of a primary side fault at the SDS, the primary OCPD can trip.
On the output/secondary side (i.e. same enclosure) will be an IMC threaded nipple to (1) 60A 2 Position Outdoor Load Center. Per "some NEC Code I don't feel like looking up right now," the (1) SBJ, (2) SSBJ, (3) GEC, and (4) EGCs for the SDS will terminate in this enclosure (i.e. the first disconnecting means of the secondary).
My question is... is there any potential for a ground loop here because I will have BOTH (1) a wire type EGC coming from the building to the SDS enclosure... and (2) a metal conduit bonding the SDS to the first disconnect, which will be grounded to a new ground rod.
I can't but wonder if I should avoid the EGC coming to the SDS from the building... and just let it be grounded at the first disconnect.
Thoughts?