Upgraded old electric meter and panel and installed a new 200 amp meter and disconnect outside. Went directly thru wall and installed new 200 amp breaker panel with lugs. Established grounding system outside at main disconnect and fed new panel with separate ground and neutral. The new breaker panel contains an existing 3 wire SER range wire. The inspector claims - because the grounding system is outside now - the new breaker panel is not “Service Equipment” and thus NEC 250.140 exception 4 no longer applies to the SER cable. He says the range wire has to be replaced now. Any recommendations? This is now a major issue with 2020 code and exterior required disconnect (which is my preference anyway)