Wiring a shop / pole barn. Got a uffer ground. Will the inspector require ground rods 6 ' apart at the disconnect?
He might, but not an NEC requirement. The compliant Ufer electrode is considered better than rods.Wiring a shop / pole barn. Got a uffer ground. Will the inspector require ground rods 6 ' apart at the disconnect?
25 ohmsI found this article written by Mike Holt, but dated 2011.
https://www.ecmweb.com/national-ele...le/20897098/grounding-and-bonding-part-3-of-3
POCO might. Our POCO won’t hook up a service without a rod.
Were this enforced, i'd wager Ufers would become rather popular.....~RJ~
Seems like a dumb POCO requirement. OP didn't say this was a service.Power company's are notorious for stepping out of bounds like that. You have no recourse, unfortunately.
Ours won't hook up without an inspection, which covers that.POCO might. Our POCO won’t hook up a service without a rod.
Ours have a completely different set of rules in addition to both (1) the NEC and (2) local amendments to the NEC.Ours won't hook up without an inspection, which covers that.
So does that mean that they require the rods or only an inspection with compliance to the NEC?Ours won't hook up without an inspection, which covers that.
The latter, unless there's something obviously wrong. The locality faxes a release to energize to the POCO.So does that mean that they require the rods or only an inspection with compliance to the NEC?
Yes same here. EI sends in a cut-in card which indicates that the installation is NEC compliant.The latter, unless there's something obviously wrong. The locality faxes a release to energize to the POCO.
Even with a passed inspection and code compliant grounding electrodes, which do not always include ground rods, our utility will not connect power unless there are two driven ground rods at the meter.Ours won't hook up without an inspection, which covers that.
Even with a passed inspection and code compliant grounding electrodes, which do not always include ground rods, our utility will not connect power unless there are two driven ground rods at the meter.
Com Ed?Even with a passed inspection and code compliant grounding electrodes, which do not always include ground rods, our utility will not connect power unless there are two driven ground rods at the meter.
That would be SO MUCH easier than the POCO having their entirely own set of rules.Yes same here. EI sends in a cut-in card which indicates that the installation is NEC compliant.
AmerenCom Ed?
Ironically, we're not allowed to land GECs in meters, although I believe that's the perfect place for exterior electrodes.Even with a passed inspection and code compliant grounding electrodes, which do not always include ground rods, our utility will not connect power unless there are two driven ground rods at the meter.
The 25 ohm deal, rumor is 2 rods do not always complyIf what specifically were enforced? Testing a single rod or installing two rods?