Once a mwbc, always a mwbc?... Or can I magically create another circuir?
Detached garage.
By code, you need a 20 amp circuit dedicated to convenience receptacle(s), and you need a circuit for lights and stuff.
You could have more, but you must have those two.
You may only run one 20 amp circuit , or you must run a sub pane!.
Which means you must run a sub panel or a mwbc (which counts as one).
You can run uf 12" underground if it is gfci protected.
So, if I run the 12-3 to a 4" box in the house, pigtail the neutral to two gfci receptacles, then run two 12-2 uf, one from each receptacle, from there underground in the same trench to the detached garage, is it now considered two circuits or still one mwbc? I am puzzled....
Detached garage.