I have a 480v 1600 amp service feeding a 600 hp VFD controlled potable water pump. The Power utility has recently shut down our substation and picked us up from another substation while they are performing work. When we tried to run out 600 hp pump after this swap over our VFD would trip out on “Fault Supply Phase” The Voltage coming from our Utility is within 3% but the Current on the Primary and Secondary side of the Utility transformer is off by more then 40% between 2 phases. This is what trips out our VFD. Luckily we have 3 other 50hp VFDs that our of a newer type and are able to handle this massive current imbalance.
When we questioned the Utility about this they told us that they are within the ANSI standards with what they are providing us :
Per ANSI Standard C84.1-1995, “Electric supply systems should be designed and operated to limit the maximum voltage unbalance to 3% when measured at the electric utility revenue meter under no-load conditions”. The supply voltage at the meter revenue point are well within the requirements even under full load conditions.
Question:
Are the Utilities only required to supply voltage balance to a certain amount but not current balance ? For the last 3 weeks we have been running a diesel pump and now it needs service and we had to bring in a 500kw generator to run our 600hp electric pump sucking 600 gallons of diesel a day. This is mind boggling to me. Yes when they switch back to their other substation which could be another month from now we will be back to normal but right now just seems like the Utility should be repairing the issue they are having that isn’t giving us the required current that we need. We are towards the end of the line downstream of their substation.
Thanks for the help
JDrais
When we questioned the Utility about this they told us that they are within the ANSI standards with what they are providing us :
Per ANSI Standard C84.1-1995, “Electric supply systems should be designed and operated to limit the maximum voltage unbalance to 3% when measured at the electric utility revenue meter under no-load conditions”. The supply voltage at the meter revenue point are well within the requirements even under full load conditions.
Question:
Are the Utilities only required to supply voltage balance to a certain amount but not current balance ? For the last 3 weeks we have been running a diesel pump and now it needs service and we had to bring in a 500kw generator to run our 600hp electric pump sucking 600 gallons of diesel a day. This is mind boggling to me. Yes when they switch back to their other substation which could be another month from now we will be back to normal but right now just seems like the Utility should be repairing the issue they are having that isn’t giving us the required current that we need. We are towards the end of the line downstream of their substation.
Thanks for the help
JDrais