Why does the code require 20 amp circuits when in Canada 15 amp circuits are the norm for everything?
I have no idea about Canada, but the stuff here that's gonna get plugged into a bathroom or kitchen will a lot of times draw more than 12 amps, which is 80% of 15 amps.

Most anything with a heating element is 1500w, or 12.5 amps
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I have no idea about Canada, but the stuff here that's gonna get plugged into a bathroom or kitchen will a lot of times draw more than 12 amps, which is 80% of 15 amps.

Most anything with a heating element is 1500w, or 12.5 amps


80% only applies to a continuous load. 15 amps will not trip a 15 amp breaker, ever.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
1875 watt blow dryer on a 15 all circuit?


Yes

125 volts @ 1875 watts = 15 amps or 8.3 ohms

8.3 ohms at 120 volts = 14.4 amps

And that is being highly optimistic. Any manufacturer can stick a 1000 watt heater inside a tube and label the exterior as 3,500kw.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
80% only applies to a continuous load. 15 amps will not trip a 15 amp breaker, ever.
Heck, sometimes 20 amps won't trip a 15 amp breaker. That's not the issue anyway, imo. The question was why 20 amp circuits, and it's because 80% of 15 amps is 12. And someone has decided 80% is enough. And 12.5 is more than 12.

And as @infinity mentioned, it's upward from there

And I know it's for continous load. And I know stuff cycles on and off. But the answer is still there.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Heck, sometimes 20 amps won't trip a 15 amp breaker. That's not the issue anyway, imo. The question was why 20 amp circuits, and it's because 80% of 15 amps is 12. And someone has decided 80% is enough. And 12.5 is more than 12.

And as @infinity mentioned, it's upward from there

And I know it's for continous load. And I know stuff cycles on and off. But the answer is still there.


Code is wrong in their inference or lack there of I think yet again...
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A 20 amp circuit for a bathroom makes sense, you could be powering a hair dryer, lights, exhaust fan, curling iron, makeup mirror, radio and what ever else your significant other or kids have plugged in.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
A 20 amp circuit for a bathroom makes sense, you could be powering a hair dryer, lights, exhaust fan, curling iron, makeup mirror, radio and what ever else your significant other or kids have plugged in.
20 amps is also a good idea in a kitchen when you have a microwave, toaster, rice cooker, air fryer, hot skillet, and a bunch of other crap on 2 circuits.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
A 20 amp circuit for a bathroom makes sense, you could be powering a hair dryer, lights, exhaust fan, curling iron, makeup mirror, radio and what ever else your significant other or kids have plugged in.


Right, if you use the code exception in 210.11 C 3.
 