Explain MBBC's is that. MAIN BREAKER BRANCH CIRCUITS ?
If you are referencing what others have posted already you mis-typed, it's MWBC - Multi Wire Branch Circuit.
Did I understand. correctly ?
Your answer is yes / 20 amp Branch circuit Breakers for circuits. 2, 4 & 6. all loaded with 8 general purpose duplex receptacles, a common neutral is allowed.
How do you balance the loads on the all. Receptacle Panel.
All receptacle CIRCUITS. ONLY. ?
As far as a general "Yes You Can" response I don't think we can give it 100%, there are a lot of variables to consider. What are the applications anticipated? Is it residential or commercial or industrial?
If each circuit of the MWBC can be expected to each reach near the capacity of the individual circuit, consideratation to sizing of the neutral of the MWBC and load capacity of it. For example if you have a large office complex, and have the suggested 2,4,6 MWBC, used on general purpose receptacles, you could have a cleaning crew that all run vacuums at same time, (depending on location of receptacles) those vacuum running individually on each branch would not overload the 20A breakers, but would overload the neutral if not upsized to carry the potential 9-12 Amps each of the vacuums.
AFA balancing the loads I don't see an issue nearly as much as I see an issue as already mentioned of neutral load, in general balance of loads is desired in relationship to panel loads, but with "general purpose" receptacle near impossible to acheive when user specific loads are applied. Also considerations to other loads to be potentially applied to panel and the locations within the panel and what phase each load is applied to, as I'm sure you're aware of.
I'm sure there are other considerations, and questions not asked or answered, that effect the answer as to use of or installation of a specific wireing method, and is why DIY instruction not given on this forum.
The short answer to your question would be "Maybe", yes you can potentially have MWBC on the 2,4,6" but the answer to all the "only IF questions" would need to be addressed. And as a designer (assuming you mean "electrical designer" not a "fashion designer") of a system you should have the knowledge of the all requirements of the system you are putting together, and the answer to your opening question can vary depending on how you answer the various requirements of the circuits you are designing, so I think it would be irresponsible to give a blanket "Yes".