mbrooke
Batteries Included
- United States
- Technician
What advantage would be reasonable in a scheme using 4 or 5 smaller power transformers operating in parallel vs 2 larger units run normally open as typically seen in the wild?
For example four 12/16/20MVA transformers vs two 40/50/60MVA 115-23kv transformers.
Similarly five 15/20/25MVA vs two 60/80/100MVA 230-34.5kv transformers.
60 and 100MVA loading respectively to allow for failure of one unit during the hottest of days (assume load transfer disabled or not available to other substations).
In running calculations the fault current is about the same for both scenarios.
I know that one large transformer is cheaper in total than many smaller transformers, however, I can not help but notice the capacity of each smaller unit is more utilized per dollar through out the in service life.
This concept tends to apply to generators, underground cables, interconnecting auto transformers, ect but rarely to distribution substation applications. Is there a technical prohibition?