Technical Feasibility of Underground AC Transmission Cable Grid

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Hypothetical question: Cost aside, would it be technically possible to operate an underground transmission grid consisting of solid dielectric cables? Burying all transmission lines 500kv and below on the east coast, west coast, UK or European Union as a discussion reference.

Would shunt reactors at each substation be enough to compensate the immense amount of reactive power? Would switching transients and risks of generator pole slipping make it simply physically impractical?

Somehow I have a feeling there are way more theoretical limitations than I am imagining atm. However, the idea of an entire system 120 volts to 500kv being placed underground with brick GIS substations has an allure to me. Outages would go down I would think.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
First thoughts, in no particular order:

Every inch of a pathway would have to be trenched or bored instead of a pole or tower set at regular distances apart.

Buried cables would be susceptible to damage from rocks, ground movement, careless digging, etc.

The cost-per-foot/mile/etc. would be much higher in both labor and materials compared to overhead lines.
 

bwat

EE
Location
NC
Occupation
EE
I know you said "cost aside", but it's hard to get past the cost difference between underground and overhead. If you've ever done a cost estimation for a new MV utility feed where overhead vs underground was evaluated it is quite significant at times. Even for small and short MV services it can be tens of thousands of dollars for underground vs next to nothing for overhead.

I'd probably agree that outage frequencies may go down... but the duration of the outages when they do occur could go in the opposite direction, so your outage-hours could be relatively the same or worse. And now everything was just more expensive.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
They sometimes have a helical insulator to cut down on losses, and a gas fill -- nitrogen or sulfur hexaflouride -- to maintain dielectric strength.
This type is often used for connecting ratio & television transmitters to their antennas. I don't know whether they're also used for electric power transmission & distribution.

This example is 5 inches in diameter and rated for 12 kV.

1625096246064.png
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
This type is often used for connecting ratio & television transmitters to their antennas.
When I saw the pic, I thought of the coax lines I've seen used at cell towers we've wired power and grounding for.

At a tour of a TV station years ago, we saw solid copper pipe inside solid copper pipe used as a transmission line.
 
They sometimes have a helical insulator to cut down on losses, and a gas fill -- nitrogen or sulfur hexaflouride -- to maintain dielectric strength.
This type is often used for connecting ratio & television transmitters to their antennas. I don't know whether they're also used for electric power transmission & distribution.

This example is 5 inches in diameter and rated for 12 kV.

View attachment 2556997
Us hams call it Hardline
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
They sometimes have a helical insulator to cut down on losses, and a gas fill -- nitrogen or sulfur hexaflouride -- to maintain dielectric strength.
This type is often used for connecting ratio & television transmitters to their antennas. I don't know whether they're also used for electric power transmission & distribution.

This example is 5 inches in diameter and rated for 12 kV.

View attachment 2556997


Thats similar to a super conducting cable a few POCOs tried:

 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I wish we had the old emojis back.
Steal them from other sites and paste them. Go crazy!
run1.gif
 