Yeah, I hear of people getting away with MC cable in cases like this, but if you read the section on MC it has the same physical damage clause. I don't think the MC armor offers much in the way of crush protection.Yes it is a violation because it’s subject to damage. For example if I leaned a ladder on that wall it could be damaged.
Solution: Use MC, it’s close to the same price.
NEC 334.15(B)
* I’m using the 2014 at the moment.
Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means.
Sent from my iPhone using Tapatalk
I sleeve romex in wire mold frequently. I discard the backing. You?Just cover with wire mold, I would use metal one not plastic though.
Yes I totally agree. It's so weird that certain things seem to be arbitrarily allowed. Like I said the whole physical damage thing, and many things in the NEC are subject to AHJ interpretation. But most inspectors agree that romex stapled securely to a piece of plywood and entering the top of a panel is reasonable. I see some electricians run the cables down the side and enter the side KOs, but I n wouldn't approve that if I were an inspector.IMO it's not much different than having exposed NM cables enter a panel in a basement and they're much lower than 8'.
Again "subject to damage" is subjective to interpretation. Leaning a ladder on it may not be all that damaging. Having a 100 pound person using ladder as it leans on it may be increased damage potential, having 350 pound person using ladder might be quite a bit more damaging potential.Yeah, I hear of people getting away with MC cable in cases like this, but if you read the section on MC it has the same physical damage clause. I don't think the MC armor offers much in the way of crush protection.
Sent from my SM-A326U using Tapatalk
Haha I literally just got done saying that. Ok, now let's talk about severe physical damage!Again "subject to damage" is subjective to interpretation. Leaning a ladder on it may not be all that damaging. Having a 100 pound person using ladder as it leans on it may be increased damage potential, having 350 pound person using ladder might be quite a bit more damaging potential.
Others may feel above a certain height maybe people will be more careful when something may be potentially damaging, but down low is subject to a lot of possibilities. Then you still can get severe enough abuse that you can still damage whatever you sleeve it in as well. So I guess wireless methods of power transmission are needed if you want to assure nothing will happen to your delivery means (conductors/cables/raceways)
Think I replied just a minute later then you, hadn't seen yours yet.Haha I literally just got done saying that. Ok, now let's talk about severe physical damage!