What's the total number of current carrying conductors in the raceway?Yes, this is from the engineered drawings. The conductors are already up-sized to #10 with a #8 neutral because they're in a common raceway, for a 20 amp circuit this seems like a waste of good money. If the run is over 85' the conductors are increased to #8 phase and #6 neutral.
Can someone try to explain this to me? These are all 20 amp circuits feeding furniture partitions with a printer receptacle at each station. (Where's the bang your head against the wall emoji?)
View attachment 2557273
I'm guessing about 15. I don't know what it means if I had to guess it's a 3-wire MWBC, 2 hots and 1 neutral. It's going to be installed as per the spec.What's the total number of current carrying conductors in the raceway? "Two multi-wire networks" means exactly what? An MWBC with two hots? Two MWBC's with 2 or 3 hots? Does the engineer have stock in a copper producer??
I am not seeing that Tom….Those specs don't allow EMT.
EMT is technically tubing not conduit but in the context of this spec. EMT is fine. Not sure where the engineering came from but the client is a foreign bank so maybe this is from their boilerplate. Does anyone know what a network is in the context of this document?I am not seeing that Tom….
No, it's an office building with cubicles. I remember these crazy spec's from the 90's but in 2021 this is a waste of someone's money.Is this a Fed project ?
This is something, a life time ago, we would price per plan and then provide a deduct for using #12 everywhere unless cct was over 150’.
If nothing else, forces EE to defend the spec.
Here, borrow mine:Where's the bang your head against the wall emoji?
price per plan and then provide a deduct for using #12 everywhere unless cct was over 150’.
If nothing else, forces EE to defend the spec.