hhsting
- Glen bunie, md, us
- Junior plan reviewer
I have 200A fused disconnect fed from 225A feeder breaker. Is their any NEC code section 2017 that says this cannot be done?
what size fuses are in the disconnect? I'm assuming the 225A is the rated size of the disconnect and not the fuses.
Whats the issue?
is it fed with 225 amp conductor or if not does it comply with tap rules?I have 200A fused disconnect fed from 225A feeder breaker. Is their any NEC code section 2017 that says this cannot be done?
is it fed with 225 amp conductor or if not complies with tap rules?
What protects your service entrance equipment from the power available from the utility company?Issue: breaker size feeding is 225A how does it protect the 200A fused disconnect?
I don't see a problem
The fused disconnect protects itself. That's why it has fuses.Issue: breaker size feeding is 225A how does it protect the 200A fused disconnect?
Right. Just like the fuses in this disconnect will protect it.The inside overcurrent protection?
The 225A circuit breaker is protecting the 200A fused disconnect. The 175A fuses are protecting everything downstream of that.The inside overcurrent protection?
???? Can you clarify what you have? Your numbers have changed a few times now. But either way... if the disconnect is rated for 225A but is furnished with 175A fuses, you don't have an issue.How? 225A breaker protects 200A fused disco? Its 200A breaker is 225A???
There is that for general applications.The fused disconnect protects itself. That's why it has fuses.
Have you ever seen a 200 amp tap made from a 400, 600... 1200 amp feeder?How? 225A breaker protects 200A fused disco? Its 200A breaker is 225A???