RF Shielding NM-B

Status
Not open for further replies.
Location
Seattle
Occupation
Electrician
Is there anything saying I can not take a piece of 10/2 NM-B, paint the jacket with RF shielding paint, pull a mylar shield over it, wrap a drain wire around the mylar, cover it all in tech flex. The drain would only connect to the line side panel. The load side would be in a plastic box and the drain would be taped over.

Or the same situation but the NM-B jacket is wrapped in a RF shielding fabric, no paint, no mylar, then a drain wrapped over the fabric, then tech flex and landed the same as above.

Thanks
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
You are holding back on too much necessary information. What is the application? What are the voltages involved?

All the rules in the NEC are mandatory or permissive. The NEC says you shall or shall not do blah, blah, blah, and anything other than that is allowed. Ultimately it's up to you and your own conscience what you do in any electrical install.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
If you're going to all that effort, why not just use MC cable or sleeve the NM in FMC? Or how about an RF filter near the item which is either causing RF or being affected by RF? Are you trying to do a TEMPEST retrofit?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Please Sweeny post in members trading post on the book about tracing emfs, it also discusses gaussmeters. The book is about to go to goodwill if you want it let me know
 
Location
Seattle
Occupation
Electrician
Ok, I was told I am not including enough information.
  • I am running 10/2 NM-B in residential homes.
  • I am running each branch circuit to a dedicated receptacle from the panel.
  • 120 volt circuits
  • I am powering high end audio gear that is very sensitive to RF.
  • Most instances there is a signal voltage of about 2mV that is being boosted either 40 to 60 times its original voltage. It is very sensitive to noise.
  • I don't like MC cable/EMT due to the parallel path of the metal case which causes all sorts of ground issues. Yes I run an extra ground and use isolated ground receptacles. This is what we do in recording studios. Most of my clients are home owners. Not studios. They do not want to use a Hubbell receptacle. They are going to replace the receptacle with a boutique one. Non of those are isolated ground.
  • I have clients asking to shield the entire room. I have to advise an RF 5ghz wave is about 7cm long. It can slip through small cracks. They would have to use paints on the inside and outside the building. Fabrics in the walls and ceilings, as well as floor. films on windows as well as curtains. And all that needs to attached to a robust ground system. Its a massive endeavor. I thought it might be easier to apply some of these treatments to the in wall cabling itself. When I exit the wall most power cables and interconnect are shielded.
What worries me the most is the shielding on the cable needs to be grounded to work. That means I have a 20 awg dead soft silver wire wrapped around the entire length too ensure the whole of the sheath will drain properly. I have experimented with this idea. I know it works. But I worry an inspector will say that drain is a conductor that is not inside the raceway. 300.3(B). But its not really a conductor. Its only terminated on one end. In the main panel. Its a bond for a Mylar or RF fabric.

Interesting I said Bond. I wonder if I would have to wrap it down with a wire that is 10AWG? Its not a raceway. But a Mylar and RF fabrics are conductive. It is technically something that could become energized?????

I have not started specifying this technique as it is somewhat unusual and I want to know if electrical inspectors have a valid reason to say I can not do as such. If they do, I wont do it. I always specify NEC/UL compliant installations. But my test in my shop show I can shunt a significant amount of noise by using Mylar/RF fabric with a drain and tech flex over the top to protect the sheath.
 
Last edited:

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
These rf signals are being amplified from the power connection and not the signal input? Seems like they need more filtering in the amplifier power supply. What is the harm of RF? How can they hear it?

Ive built 3 shielded rooms and it is not easy (it is not my area of expertise, but i seemed to know more of the issues than anyone else so i was voluntold). I was trying to get 100dB of attenuation and it was more like 30. Used foil on the walls and ceiling. Floor was metal pan. The door is the bugger, especially if you want years of service.

All power and signal lines had rf filters at the foil perimeter. Even if you shield most of the branch circuit, how do you keep rf from coupling to it in the panel or from other cables you didnt shield that couple through the neutral bar or power bus.
 
Location
Seattle
Occupation
Electrician
Filters on equipment can dramatically reduce dynamics and life. Puts a veil over the music.

RF acts much the same when coupled to the power line. It creates a distortion that blocks your ability to hear full frequency. I'm not saying that technically correct. You hear it when you get rid of it. Details you never heard in a record are there. A stand up bass or violin will sound more like its in the room with you. Not like its on a record.

There are some filters that block RF. On some systems they work well on preamps and digital equipment. That is one place were I have heard a back to back, filtered and not filtered. Its very apparent.

I have never heard a filter improve an amplifier. The amp always sound better direct to the wall. So I want to shield the power to those outlets for sure.

And yes you have a point, any break in the shield and noise can get back in. A plastic plate over the duplex could let it in. The duplex itself could let it in. It gets all over. My hope is to limit the expose by shielding as much as I can. All the in wall wires are antenna.
 
Location
Seattle
Occupation
Electrician
I buy it through Rio Grand. A online jewelry shop. Its not signal wire. Its a drain. I could use copper too. Non of that is very pure eithet. The copper that is. Most is cheap china wire pulled through high speed dies with all sorts of crystal boundary. Real, pure copper cost $16 to $40 a foot for 10/2. But non is UL for use in the USA.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Sounds like you need to install a technical power supply and shield the output side. No matter what you do to the branch circuits, there will be RF introduced on the line side of those branch circuits. However 647.3 does not permit them in dwelling units. I understand there are some cord and plug connected ones that can be used as long as everything is connected by cord and plug.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I buy it through Rio Grand. A online jewelry shop.
Never heard of them.
Its not signal wire. Its a drain. I could use copper too. Non of that is very pure eithet. The copper that is. Most is cheap china wire pulled through high speed dies with all sorts of crystal boundary. Real, pure copper cost $16 to $40 a foot for 10/2. But non is UL for use in the USA.
That china stuff is so inferior.
 
Location
Seattle
Occupation
Electrician
Hopefully this can not get too sidetracked. I understand a lot of people get consternation over rich people going to crazy extremes with their hobbies. I am trying to assist them in getting the most from what they are doing. I think I touched on a important point in my additional comments. If I do this, am I actually bonding a metalic object that could become energized and 20 AWG would be to small. Would 250.96 apply. 250.102? Table 250.122?
 

Russs57

Senior Member
Location
Miami, Florida, USA
Occupation
Maintenance Engineer
If you use a high quality amplifier and feed it with a perfect 60 hertz sine wave....you will get high quality power.

You might want to consider the distortions that the audio equipment causes.

I like "balanced power" myself. Anything remotely digital has an isolation transformer and a filter in front of it.

I like vinyl and tubes.
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
So, I assume you're running 10/2 to a regular 20A outlet? To keep the impedance as low as possible?

What about 10/2 MC cable? Isn't that providing some shielding due to the outer metal cover and it has a full size ground?
 

Todd0x1

Senior Member
Location
CA
So you're doing this fancy wiring, but what about RF shielding the utiliy's feeders to the structure and isolating it from the neighbors with its own transformer, etc?
 