Concrete encased electrode for residential home?

Status
Not open for further replies.

anbm

Senior Member
Is new residential home typically be built with concrete encased electrode? Most of the time I only saw a ground rod was driven by the elec. panel and bond to panel main ground bar but not sure if the panel also bond to concrete encased electrode (if exist)...
 

kwired

Electron manager
Location
NE Nebraska
As rule is written, if qualifying rebar is present in the footing, you must use it, exception for existing construction

If no qualifying rebar 20 feet or more of 4 AWG in the footing makes it a CEE but that is optional.

There is coated rebar as well as some fiberglass reinforcement that sometimes could be used - those obviously are not qualifying for a CEE.
 

anbm

Senior Member
As rule is written, if qualifying rebar is present in the footing, you must use it, exception for existing construction

If no qualifying rebar 20 feet or more of 4 AWG in the footing makes it a CEE but that is optional.

There is coated rebar as well as some fiberglass reinforcement that sometimes could be used - those obviously are not qualifying for a CEE.
UFER ground is an option for new residential house?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Here is the section

250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system. Where none
of these grounding electrodes exist, one or more of the
grounding electrodes specified in 250.52(A)(4) through
(A)(8) shall be installed and used.
Exception: Concrete-encased electrodes of existing buildings or structures
shall not be required to be part of the grounding electrode system where
the steel reinforcing bars or rods are not accessible for use without
disturbing the concrete.
 

anbm

Senior Member
"Where none of these grounding electrodes exist, one or more of the
grounding electrodes specified in 250.52(A)(4) through
(A)(8) shall be installed and used."

You have to read 250.52.

-Hal
Got it, but I assume we can still have both ground rod plus ufer?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The resistance of a ufer ground is much much less than a ground rod. Since both are basically for lightning protection, all is needed is a ufer. If you can’t determine why the code does not require ground rods with a ufer, ask and I can explain it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As kwired Et al. stated if the rebar qualifies as a CEE then a CEE must be used. There are two ways to use a CEE one is using the rebar the other is using the aforementioned 20' of #4 or larger bare copper, your choice.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Is new residential home typically be built with concrete encased electrode? Most of the time I only saw a ground rod was driven by the elec. panel and bond to panel main ground bar but not sure if the panel also bond to concrete encased electrode (if exist)...
And it’s not just residential homes, it’s any occupancy.
 

kwired

Electron manager
Location
NE Nebraska
UFER ground is an option for new residential house?
1641343472161.png

Note how it says all electrodes described in A1 through A7 must be used if they are present. If a qualifying CEE is not present you do not have to make one. Still is an option however to make one - that is often where the 20 feet of #4 copper is used for a CEE. Same goes for qualifying water pipe electrode or building steel. If present you must use them but are not required to add them if they are not present. That covers items 1 through 3. Items 4 through 7 generally won't exist unless you intentionally add them. If items 1 through 3 don't exist you will be adding something because you still need at least one grounding electrode.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The NEC only requires use of a UFER in new construction if the footer construction provides for one.
You can get into a real bind if the rebar qualifies to be a UFER but no connection was made to it before pouring. You then have to chip out concrete to make an attachment point.
Some jurisdicrtions, however, require a UFER in all new construction, even if you have to lay copper wire in the footer to create one. If you skip this step in those areas you are really in trouble.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
NC is behind the times on this one. I wish they would require it but what they say is when the electrician gets to the job the concrete encase electrode is not available so you don't need it.

When I was running the business we always installed a concrete encase electrode unless the builder poured without calling me. I had to stay on top of the situation.
 
Status
Not open for further replies.
Top