Details 200 amp aerial service a 90 amp breaker feeding garage subpanel approximately 100ft UG in PVC piping. The path is from house basement panel out of building and buried about 80 ft to attached garage outdoor routing is due to many finishes in this split level home. This garage in future may or may not have a hot tub or split AC unit, garage lighting plugs currently fed from 200amp panel 20 amp breaker from original construction. Size is 2 car garage
Was going to use 90amp breaker in main to feed sub panel. Supply house said 2-2-4-6 mobil home cable is appropriate. (What they stocked)
Checked into #6 ground according to 250.122 table this is fine
For neutral I'm a bit confused 220.61 max load neutral to ungrounded conductor determines size.
So i guess you could have an odd situation that all loads would be on "A" phase and you could put 90 amp on Neutral so 2-2-2-6 would be required.
Permitted reduction seems only to be with cooking and dryers
Am I correct in thinking 2-2-2-6 is the necessary cable for this application
Was going to use 90amp breaker in main to feed sub panel. Supply house said 2-2-4-6 mobil home cable is appropriate. (What they stocked)
Checked into #6 ground according to 250.122 table this is fine
For neutral I'm a bit confused 220.61 max load neutral to ungrounded conductor determines size.
So i guess you could have an odd situation that all loads would be on "A" phase and you could put 90 amp on Neutral so 2-2-2-6 would be required.
Permitted reduction seems only to be with cooking and dryers
Am I correct in thinking 2-2-2-6 is the necessary cable for this application