Customer's AC unit when it kicks on, dims lights and sometimes trips the breaker. And when we turned on the breaker today, it immediately trips several times. Circuit cap. 19.5 a, max breaker: 45 amps. on label. It is on a 40 amp 20 yr old breaker run with #8 copper wire. Sometimes the breaker hums when we turn it on.
He says it started doing these two things after we worked there. He is getting ready to sell and had asked us to make the house code compliant. Several twins (tandems) were in the panel that did not allow twins. Plus someone had added a wide variety of breaker brands over the years. And this 200 a panel was one of the most crowded packed panels I have seen. We installed a sub panel.
Today we checked voltage and amperage at the outside AC while it was running 118v and about 17 amps on each leg. The 40 amp breaker felt warm but not hot. We disconnected the AC outside at disconnect, and of course the breaker never tripped when turning it on. Owner says he had his HVAC guy check it and said it was fine.
The lighting circuit that dims each time the AC starts up is in our new subpanel. Just for experiment, we temporarily ran a 12-2 from the sub over into the main panel and powered up the lights using the main panel and turned on the breaker, unfortunately the bedr and liv lights still dimmed.
I'm going to install a 45 a breaker and run a coil of #8-2 (that is in my shop) from the breaker, out the door to the AC the next chance I get. If my new wire temporary run and new breaker makes it good, I guess it has to be the AC or a nick in the house wiring somewhere...?
Any ideas ? Thank you.
He says it started doing these two things after we worked there. He is getting ready to sell and had asked us to make the house code compliant. Several twins (tandems) were in the panel that did not allow twins. Plus someone had added a wide variety of breaker brands over the years. And this 200 a panel was one of the most crowded packed panels I have seen. We installed a sub panel.
Today we checked voltage and amperage at the outside AC while it was running 118v and about 17 amps on each leg. The 40 amp breaker felt warm but not hot. We disconnected the AC outside at disconnect, and of course the breaker never tripped when turning it on. Owner says he had his HVAC guy check it and said it was fine.
The lighting circuit that dims each time the AC starts up is in our new subpanel. Just for experiment, we temporarily ran a 12-2 from the sub over into the main panel and powered up the lights using the main panel and turned on the breaker, unfortunately the bedr and liv lights still dimmed.
I'm going to install a 45 a breaker and run a coil of #8-2 (that is in my shop) from the breaker, out the door to the AC the next chance I get. If my new wire temporary run and new breaker makes it good, I guess it has to be the AC or a nick in the house wiring somewhere...?
Any ideas ? Thank you.