Status
Not open for further replies.

KronikT

Member
Location
Colorado
Occupation
Electrical contractor
I am rewiring a condo on the 22 floor of a high rise so everything is run in emt or mc.
My client doesn’t want receptacles in her backsplash. Instead she wants plug mold just under the upper cabinets.
I’m having issues trying to find plug mold that is compatible with mc in this application. Can someone point me in the right direction?
 
Welcome to the forum.

Doesn't hardwired Plugmold have 1/2" KOs on the back? (yes, see pic) Any standard MC connector should work.

1659483523097.png
 
The ones I have done has all the parts you need. You need to get the kit. Using the end fed is optional. I agree it's not attractive.
 

Attachments

  • Screenshot_20220803-051534.png
    Screenshot_20220803-051534.png
    145.6 KB · Views: 8
  • Screenshot_20220803-051441.png
    Screenshot_20220803-051441.png
    83.3 KB · Views: 8
The problem with MC and the built in KOs in the back is the regular pop on mc connectors stick too far into the plug mold.

A fitting like this may work. I've used them when hanging track light with a live end feed.
steel_fastlock_conn.jpg
 
I still use individual Wiremold boxes for under-cabinet receptacles.
Do you use one of the channel KOs to bring wire in? Wouldn't be a real cable KO

But truth be told, that's what I use to make up plugmold instead of a plugmold end feed

Reason is the end feed is tall, and visible under cabinet. Wiremold j-box is the same depth as plumold.

I don't suggest it anywhere that the inspectors actually do their job.Screenshot_20220803-103036_Gallery.jpg
 
Do you use one of the channel KOs to bring wire in? Wouldn't be a real cable KO

But truth be told, that's what I use to make up plugmold instead of a plugmold end feed

Reason is the end feed is tall, and visible under cabinet. Wiremold j-box is the same depth as plumold.

I don't suggest it anywhere that the inspectors actually do their job.View attachment 2561619
Hey that track you have your low volt feed in looks pretty slick. Can I ask what your using and where you got it
 
Do you use one of the channel KOs to bring wire in? Wouldn't be a real cable KO
No, I just use individual Wiremold boxes with receptacles and plates, with the narrow end butted up to the back skirt.

That leaves room for the LED ribbon which I place about 1.5" from the front skirt with side skirts V-cut where needed.

I just called my recent customers and they said I could come by tomorrow to take a few pictures of this installation.

1659542650032.png
 