ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
I am working on a PV system design to connect to a 480/277V service; the junction box where we will be interconnecting does not have a neutral and it is over 100' (underground run) from the disconnect. One of our field guys has verified that all three phases are 277V to ground, so it isn't ungrounded or corner grounded. The inverters do not require a neutral, so the missing neutral wouldn't be a problem, except that the system is in a jurisdiction that requires a PV meter and the meter needs a neutral to work (verified by the utility).
I know next to nothing about zigzag transformers, but I looked them up and what I am seeing is that they can be used to create a neutral for an ungrounded service, but this one isn't ungrounded. How should I create the neutral for the meter?
I know next to nothing about zigzag transformers, but I looked them up and what I am seeing is that they can be used to create a neutral for an ungrounded service, but this one isn't ungrounded. How should I create the neutral for the meter?