This is first time for me dealing with instantaneous water heaters. I have a quadraplexes type building that will be divided into 4 tenants. They want instantaneous water heater in each tenant rated at 24KW at 240V. I'm coming up with a total load of about 38KW in each tenant, which puts me at 200AMP 240V single phase panel at each tenant. The issue is that this particular area is mostly residential where this is being built and everything is pole mounted transformers. Should i provide an 800AMP single phase service out that will probably require a pad mounted transformer from utility? Or possibly do a 600Amp 208V 3 phase service that will use a pole mounted transformer but will derate the waterheater by 25%. If you don't mind sharing your opinions on this and what you think is a good options to deal with this. Thank you!!