We were recently red tagged for voltage drop, inspector cited
"C405.9 Voltage drop across combination of feeders and branch circuits cannot exceed 5%" --2020 ECCC of NY
Where is this in the code?
I thought voltage drop was only a fine print note.
It was an easy fix so we pulled in #8's and got it passed to keep moving, but I have always been told voltage drop was just a suggestion or 'FPN'.
Where and when is this in the code in NY state?
Thank you all for your replies.