I have a customer in a single family residence who would like me to add a 20 amp 120 volt circuit to their 200 AMP Main Breaker Challenger Panel. The panel is extremely full, and as a result their is no room on the neutral bar. What is the best way to alleviate this problem? I was wondering if I could add a new ground bar, and run a #6 ground (Or would have to be a #4) between the two bars, and then relocate some of the ground wires over to the new ground bar to create some space. If this is even a possibility, do I have to have a ground bar that is rated for a Challenger Panel? Does anyone make ground bars that are listed for Challenger Panels, or would any ground bar due as long as I drill and tap it?
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I have seen many filled panels that over time with a circuit here and there get filled for no reason.

IMO, go through the circuit directory and see which circuit/s you can add together.

Sometimes you will have unnecessary dedicated circuits. Smoke detectors, one circuit just for the bathroom light, one circuit just for the bedroom....

IMO, you will find such circuits that you can connect together and use one circuit breaker to create your neutral opening.

Can you share your circuit with another circuit?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Generally you can double or triple up the wires under a screw if they are EGs, Read the labels. You can also pigtail several of the EGs together.
I've used about any Mfg EG bar as needed. Scrap paint, a jumper to the Neutral bar, about anything.
If the bar is only for grounds, there is no need for a jumper to the neutral bar.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
You don't need a Challenger ground bar. But Eaton is the successor to most Challenger panels I've seen, and an Eaton groundbar may be slightly more likely to match up to exisiting mounting holes in the panel.
 

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
I guess I really don't need to have it by itself. I guess was trying to prevent something other than refrigerator possibly tripping the gfci breaker. The refrigerator will be located in the garage.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
If the bar is only for grounds, there is no need for a jumper to the neutral bar.
I agree here.
I also have a 200 amp Challenger panel in which I'm adding washer and dryer circuits.

I'll be adding a ground bar on each side for grounds only, where I marked in green.
Drill and tap to mount, no jumpers to neutral bar Screenshot_20221025_074835_Gallery.jpg
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Well that may help you correct the egc’s that look to be landed under the same screw as the neutral conductors.
And you will need a wire to the added ground bars if the bonding screw is not there.
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Well that may help you correct the egc’s that look to be landed under the same screw as the neutral conductors.
And you will need a wire to the added ground bars if the bonding screw is not there.
Yes, I have to add the ground bars to get relief from the existing neutrals and grounds sharing holes
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Well that may help you correct the egc’s that look to be landed under the same screw as the neutral conductors.
And you will need a wire to the added ground bars if the bonding screw is not there.
Unless you're landing grounded conductors on the added ground bar, you won't need any wire/jumper added.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
Buy a small ground bar kit and drill and tap to the can. The neutral bar is already bonded to the can. Does Cutler-Hammer make tandem breakers that are listed to use in Challenger panels? That would free up some space for your additional breaker.
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
You
Unless you're landing grounded conductors on the added ground bar, you won't need any wire/jumper added.
You would if the EGC bars are just floating without connection to the grounded conductor in some fashion. I take it that this is the service panel.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
You

You would if the EGC bars are just floating without connection to the grounded conductor in some fashion. I take it that this is the service panel.
They wouldn't be floating as they are mounted directly to the can. They don't have to connect to the neutral bar as it should be bonded to the can already.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Buy a small ground bar kit and drill and tap to the can. The neutral bar is already bonded to the can. Does Cutler-Hammer make tandem breakers that are listed to use in Challenger panels? That would free up some space for your additional breaker.
Is the wall of the can really thick enough to get the 250.8(A)(5) two threads engagement?

While it isn't the prettiest thing in the world, the easiest thing to do is remove some ground wires and pigtail them to a single hole freeing up however many the OP needs. This was suggested by an earlier poster.
 