Does NEC require all EGC's in a box to be tied together even if the far end of one EGC is tied back to the panel bus bar?
Example (resi all plastic):
2-gang w/ one 3way switch and one duplex receptacle with ckt for receptacle.
Across the room is a 1-gang 3way switch with it's own ckt for power (lights).
So, you see how this goes, one 14-3 home-runs between the two boxes, the EGC for that 3way wire is tied to ckt EGC in the 1-gang box.
Does the 14-3 EGC in the 2-gang need to be tied to the EGC of the ckt that feeds the receptacle?
The 2-gang 14-3 EGC would land on the yoke of the switch, but I don't see where NEC requires the "all in box" must be tied together.