2020 NEC 210.12(A) - " All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling units shall be protected by any of the means described in 210.12(A)(1) through (A)(6)"I fail to see a AFCI requirement for dwelling unit bathrooms in 2017-2023
What code cycle are you reading from?210.12(A) does not mention bathroom. AFCI is not required in dwelling unit bathrooms.
Ron
This is what I see in 2020 code book. No mention of bathrooms.2020 NEC 210.12(A) - " All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling units shall be protected by any of the means described in 210.12(A)(1) through (A)(6)"
2020 includes bathrooms.
It does not appear you are quoting the actual NEC.. The rooms are listed.2020 NEC 210.12(A) - " All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling units shall be protected by any of the means described in 210.12(A)(1) through (A)(6)"
2020 NEC. It doesn't matter. AFCI is not required in bathrooms.What code cycle are you reading from?
First off I think is was a misprint, 2nd what makes you think the handbook is not the NEC? It’s just an NFPA NEC code book with commentary.The Handbook is not the actual NEC.
If you look at the actual Code ( NFPA 70 )you will see the wording is more specific,.
As pointed out in Post #9, bathrooms are not listed in the requirement.
Depending on what he was quoting from the Handbook, the commentary is not code and is not enforceableFirst off I think is was a misprint, 2nd what makes you think the handbook is not the NEC? It’s just an NFPA NEC code book with commentary.
I agree with that. But the commentary is from the writers which helps to illustrate intent.Depending on what he was quoting from the Handbook, the commentary is not code and is not enforceable
No. Who uses the kitchen sink as a toilet, or the toilet to wash dishes in??????…..or similar rooms or areas shall be protected.
Seems inclusive enough in the verbiage to require AFCI in bathrooms