Thank you for your reply, what would your recommended procedure be? Amp meter? Analog meter like a Tripplett? One lead to the water the other to the perimeter ground? Thank you again.I would first measure the voltage where the homeowner feels it. Then I would start cutting off circuits to see if the voltage is affected by the service for the house. If not then there may be a power company issue leaking to ground.
You also need to check if everything is properly grounded.
Make sure there is an equipotential bond for the pool. Use your meter on continuity, you may have to make a long lead for it, and check all equipment, metal objects, such as ladders, handrails, diving boards, etc. Check from each to the bond ring/grid. There is more you can do, but this will be a good start. Also, make sure there is a water bond. You said "tingling near the skimmer" so the bond may be missing to the water.Good morning, What is the best way to check for stray voltage in a swimming pool? The homeowner feels a tingling near the skimmer, I could not reproduce it.
Stray voltage won't trip a GFCI.Test the GFCI's,. Everything should be on a gfci, except possibly a heater, if one.
I would not let anyone near that pool until this is resolved.Good morning, What is the best way to check for stray voltage in a swimming pool? The homeowner feels a tingling near the skimmer, I could not reproduce it.
No, but it's a process of elimination.Stray voltage won't trip a GFCI.
digi volt meter I would assume.Good morning, What is the best way to check for stray voltage in a swimming pool? The homeowner feels a tingling near the skimmer, I could not reproduce it.
What? Everything is bonded at the pool to effectively eliminate resistance between points.everything being bonded at the pool, does not eliminate stray voltage potential, if such bonding has resistance between points.
yes. also please include your credit card number.@mike5456
Would you please update your profile to include your occupation and general location?
Why would testing the GFCIs help to find where the stray voltage is coming from?Test the GFCI's,. Everything should be on a gfci, except possibly a heater, if one.
And when one bonding wire/connection comes loose, corrodes, breaks off, [add a reason here], then bonding becomes not 100%, which can then cause the volt meter to have a reading.What? Everything is bonded at the pool to effectively eliminate resistance between points.
Well technically it is no longer bonded if the path is opened or gains resistance.And when one bonding wire/connection comes loose, corrodes, breaks off, [add a reason here], then bonding becomes not 100%, which can then cause the volt meter to have a reading.