Voided UL listing

Status
Not open for further replies.

Crash117

Member
Location
Nevada
Occupation
C-2 electrical contractor/owner operator
Hello all. New user to the forum here. Been electrician for 25 years and last 10 a contractor. I have a question regarding UL listing on not matching breaker type to sub panel type used. I recently was called out to repair a HO accident in a brand new home. He was mounting a mirror and drilled a wire causing arc fault trip in garage sub panel. Upon arriving, found sub panel to be homeline but every breaker in it was Eaton. I informed him this would void his UL listing in his panel and potentially be an issue if he ever had to claim home insurance. Since the builder was still constructing homes in the area he came over and I showed him the issue. He told me I’m wrong but I feel if he has his EC doing this in all homes in the area, there could troubles ahead if any owner has electrical issues and needs to claim insurance. As a side note, this home passed new construction inspection and sticker was posted on panel door. Thanks in advance for comments.
 

Bwas

Member
Location
Florida
UL listing is void unless the panel is listed for using those breakers. I'm not sure of the details but don't think i have ever seen a panel listed for another manufacturer's breakers. Kind of surprised the AHJ allowed it but he probably didn't know the difference.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

You are correct, and there is no excuse for such an error.

The electrical should enforce the correction.
 

Crash117

Member
Location
Nevada
Occupation
C-2 electrical contractor/owner operator
Yes inspected and passed. Sticker on Homeline panel with Eaton breakers stamped and approved. I feel I should call AHJ and raise this concern with them. I did get pictures of said panel as well.
 

retirede

Senior Member
Location
Illinois
This may not be an issue. Eaton makes "classified" breakers for a number other brands and those breakers are not a listing violation when used in any panel that they have been classified for use in.
Eaton Classified breakers

Aren’t those quite a bit more expensive than non-classified? I wouldn’t expect to see a panel full of them unless there was no other option. Especially in new construction.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Aren’t those quite a bit more expensive than non-classified? I wouldn’t expect to see a panel full of them unless there was no other option. Especially in new construction.
No idea of the costs, but high costs does not equal a code violation.
 

Crash117

Member
Location
Nevada
Occupation
C-2 electrical contractor/owner operator
As of course this is new construction, nearly all breakers in this panel are combo arc/gfi breakers except for a couple double pole breakers. I’m not familiar with classified breakers for multi use. I’ll have to see if customer will allow a return visit for a follow up inspection. If they say yes, I’ll prepare documentation from both Square D and Eaton about panel and breakers in question.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
No idea of the costs, but high costs does not equal a code violation.

I’ve bought them before, the price was competitive with any other brand. The price recently has been inflated.

I know all the residential guys here have been using whatever they could get their hands on the last year or so. I’ve seen a lot of mis-matched load centers and breakers going out the door of the supply houses. I have to assume inspectors are just letting it go now.

I’ve been buying a lot of breakers online lately because the brokers are hoarding them and charging astronomical prices. I needed several BR220 & BR230 GFI’s last year, and paid $300/ea.


Sent from my iPhone using Tapatalk
 

Crash117

Member
Location
Nevada
Occupation
C-2 electrical contractor/owner operator
I’ll have to contact AHJ and see if they’ve been letting things like that go due to supply problems. I would hope not but finding out for sure is a must
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
As of course this is new construction, nearly all breakers in this panel are combo arc/gfi breakers except for a couple double pole breakers. I’m not familiar with classified breakers for multi use. I’ll have to see if customer will allow a return visit for a follow up inspection. If they say yes, I’ll prepare documentation from both Square D and Eaton about panel and breakers in question.
Not sure that they are for multi use...they are classified and tested to be used in specific panels just like the OEM breakers are. A breaker classified for use in a SquareD panel cannot be used in a GE panel.
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
Not sure that they are for multi use...they are classified and tested to be used in specific panels just like the OEM breakers are. A breaker classified for use in a SquareD panel cannot be used in a GE panel.
The eaton BR style classified hit any BR style you can think of they have a chart with what busings they are listed for. There are qo style ones and bolt on classified ones that are more specific. I've had to use the classified afci before to get a microwave to hold on a new house last year and it was classified for multiple brands panels.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Not sure that they are for multi use...they are classified and tested to be used in specific panels just like the OEM breakers are. A breaker classified for use in a SquareD panel cannot be used in a GE panel.
Well, actually that depends.

This is the issue. Eaton has "Classified" breakers for use in SPECIFIC panels from competitors or brands that Eaton has taken over through the years, as listed in the documentation that comes with the breakers. But if you have the Classified that they have for many of the different brands, AND your panel is on the list, then the same breaker, called a "CL" Series, is used for these multiple brands of panels; i.e. Siemens, Crouse Hinds, Murray, T&B, GE, Bryant, AND Square D Homeline. The CL breakers are all the same, then they have a DIFFERENT Classified breaker for Square D QO panels.

Here is the list of panels that can the Eaton CL breakers can be used with;

It should be noted that although the BR Series breakers WILL also fit in the same panels, they are NOT listed for use that way. BR breakers can only be used in Bryant panels.

Now, ALTERNATELY, a Square D Homeline panel is NOT listed for use with anything except Square D Homeline breakers, and the Classified breakers are technically sold as "REPLACEMENTS" to the original. So when the panel is initially installed, at least ONE of the breakers must be actual Homeline to avoid negating the UL listing of the panel. Usually if there is a Main breaker, that qualifies.

The only mfr that offers Classified breakers is Siemens, who has a Classified breaker for Square D QO panels only
 

norcal

Senior Member
Well, actually that depends.

This is the issue. Eaton has "Classified" breakers for use in SPECIFIC panels from competitors or brands that Eaton has taken over through the years, as listed in the documentation that comes with the breakers. But if you have the Classified that they have for many of the different brands, AND your panel is on the list, then the same breaker, called a "CL" Series, is used for these multiple brands of panels; i.e. Siemens, Crouse Hinds, Murray, T&B, GE, Bryant, AND Square D Homeline. The CL breakers are all the same, then they have a DIFFERENT Classified breaker for Square D QO panels.

Here is the list of panels that can the Eaton CL breakers can be used with;

It should be noted that although the BR Series breakers WILL also fit in the same panels, they are NOT listed for use that way. BR breakers can only be used in Bryant panels.

Now, ALTERNATELY, a Square D Homeline panel is NOT listed for use with anything except Square D Homeline breakers, and the Classified breakers are technically sold as "REPLACEMENTS" to the original. So when the panel is initially installed, at least ONE of the breakers must be actual Homeline to avoid negating the UL listing of the panel. Usually if there is a Main breaker, that qualifies.

The only mfr that offers Classified breakers is Siemens, who has a Classified breaker for Square D QO panels only
BR is listed for Challenger also, Eaton CL is the classified line.
 

retirede

Senior Member
Location
Illinois
No idea of the costs, but high costs does not equal a code violation.

I understand that.

My point is that it’s unlikely those breakers are classified for the panel. If the same contractor is building a bunch of houses in that area, it sounds like tract homes, and they won’t spend an extra dime if they can help it.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
This whole issue gets interesting in the following way:
UL lists specific Classified breakers which are UL tested and approved for use in other manufacturers' panels.
But the documentation for those target panels does not usually approve or even mention the use of another manufacturer's Classified breakers in those panels.
Does the UL approval of use of Classfied breaker, A, is panel B constitute an ammendment to the original UL listing of panel B, which did not include testing with A breakers?
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
I don't understand why with today's technology that breakers can't be made to be non-interchangeable if they are not listed to be installed in other panels. This has always blown my mind. "Well the breaker fits perfectly in the panel?" "I know it does, but it could create a safety hazard if we put it in there." Brilliance at work!
 