ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
300.2(C) allows AC and DC conductors in the same raceway as long as they all have insulation ratings as high as the highest circuit voltage. 690.31(C) allows DC conductors in the same enclosure enclosure as inverter output conductors when they are separated by a barrier or partition. Does the partition obviate the need to have the insulation all at least rated as high as the maximum voltage, i.e., can there be 1000VDC circuits in with inverter output circuits in 600V THWN-2 if there is a barrier?