solidgroundconstruct@gmai
Member
- Location
- 44145
- Occupation
- electrical contractor
We installed underground RHH-RHW wire from the pole to 200A box then continued that into the 200A service panel inside Inspector turned it down, stating 300.3 in table310.104(A) Also 300.18 shall be installed complete between outlet, junction,or splicing points prior to the installation of conductors. Your panel and meter base are certainly splice points and or junctions. The conductors in question are carrying unprotected current and without a disconnect, other than pulling the meter.
This under ground wire was coated and crushproof 600V rated 2 hour fire rating. 90deg C. . RHW cables can be used for raceway, duct, direct burial, and aerial installations. These wires are suitable for installation in raceway, duct, direct burial, and aerial installations in accordance with National Electric Code and other general-purpose wiring applications.
We then installed three wire 2/0 copper and he turned that down also stating the same code above
we see no difference in Applications. 4/0 AWG Aluminum XHHW/ XHHW-2 wires are primarily used for power distribution; and are sometimes referred to as feeders. They may be used in wet or dry locations with conductor temperatures not exceeding 90°C and may be used in conduit and recognized raceways as specified in the National Electrical Code. Need your advise please
This under ground wire was coated and crushproof 600V rated 2 hour fire rating. 90deg C. . RHW cables can be used for raceway, duct, direct burial, and aerial installations. These wires are suitable for installation in raceway, duct, direct burial, and aerial installations in accordance with National Electric Code and other general-purpose wiring applications.
We then installed three wire 2/0 copper and he turned that down also stating the same code above
we see no difference in Applications. 4/0 AWG Aluminum XHHW/ XHHW-2 wires are primarily used for power distribution; and are sometimes referred to as feeders. They may be used in wet or dry locations with conductor temperatures not exceeding 90°C and may be used in conduit and recognized raceways as specified in the National Electrical Code. Need your advise please