I understand that 50a Home Depot receptacles are failing, due to overheating. Especially when when the dryer, electric oven and hot hot water tank is calling.
Is there a standard that being discussed about EV home charging?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I understand that 50a Home Depot receptacles are failing, due to overheating. Especially when when the dryer, electric oven and hot hot water tank is calling.
Is there a standard that being discussed about EV home charging?
Don’t know why the receptacle would fail when other loads that are not connected to it are one.
 

retirede

Senior Member
Location
Illinois
What's your source for this? News to me. Also, I've never seen a Home Depot receptacle. They generally sell name brands from what I've seen.

Google “Melted 14-50R”. You’ll get dozens of results from various EV owners forums. The most common culprit is the $9 Leviton receptacle commonly sold in big box stores.
 

macmikeman

Senior Member
If they can beef up breakers just for EV and PV systemsI'm all for it. I have on my iPod lot of pictures of burnt up circuit breakers that were feeding one or the other of the two I mention. Contractors put in #2 cu conductors to Tesla wall chargers and the 100amp breakers feeding melted. Checked connections and all were spec or tighter. And now Tesla doesn't sell 100 amp chargers any longer so I'm feeling fairly certain it must have been more than just the ones I have looked at. Not as often I have seen similar cases with grid tied PV installs but on those , I am not convinced that the connections at the branch circuit breaker were properly torqued. I found very loose connections at breaker terminal lugs on more than one case I have investigated .
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If they can beef up breakers just for EV and PV systemsI'm all for it. I have on my iPod lot of pictures of burnt up circuit breakers that were feeding one or the other of the two I mention. Contractors put in #2 cu conductors to Tesla wall chargers and the 100amp breakers feeding melted. Checked connections and all were spec or tighter. And now Tesla doesn't sell 100 amp chargers any longer so I'm feeling fairly certain it must have been more than just the ones I have looked at. Not as often I have seen similar cases with grid tied PV installs but on those , I am not convinced that the connections at the branch circuit breaker were properly torqued. I found very loose connections at breaker terminal lugs on more than one case I have investigated .
Listed breakers must carry their full load forever in open air at 40°C without damage to the breaker or the conductors. Would expect to see some issue other than the breaker.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
I have no first-hand experience, but probably equivalent.

The Hubbel and Bryant heavy duty ones can run up to $100 depending on where you buy them.
$213 on Grainger site.

What is so special about them to make them so much higher than others with same configuration?
 

retirede

Senior Member
Location
Illinois
$213 on Grainger site.

What is so special about them to make them so much higher than others with same configuration?

The EV community has created a huge demand for these, thus the price hikes. They were $98 at Grainger last October.

Here is a comparison:

8259430de9900c5e1f13bbf579f39405.jpg


They also differ on the wire side. The Leviton has screwdriver clamp screws that twist directly on the wire, while the Hubbell has Allen screws with saddles.
 