The POCO does it all the time.
OK tell Cali pocos to change they got money right?I am of the opinion that the way the utilities supply power is causing problems with the power gradients around homes ?
OK tell Cali pocos to change they got money right?
Not unthinkable, and allowed by the NEC. Transformers don't have to be installed as SDSs, you can solidly connect the primary neutral to secondary neutral instead.Solid electrical connection from the primary neutral to the secondary neutral. Such a connection is unthinkable and unheard of in the industrial, commercial and residential electrical engineering fields.
eh, find something else to worry about.....Solid electrical connection
from the primary neutral to the secondary neutral. Such a
connection is unthinkable and unheard of in the industrial,
commercial and residential electrical engineering fields.
Or run an ungrounded system. Both will increase costs over an MGN and it's easy to write off the cost aspects until you consider it is us that would pay for it not the utility.I don't know how old the article is, but I know I read it more than 20 years ago. I think it was posted on an old forum on eng-tips.com
Either in that forum or in the continuation of the article that is not posted here, it was mentioned that the solution to the re-grounding problem is for the power companies to run five wires instead of four, three phase wires, the neutral wire which would then be insulated and isolated from ground except at its single grounding point where it originates, and a protective earth wire. Just like the way we do it in commercial/industrial wiring. They would then have to treat the neutral just as they do a phase conductor when working on the system - assume it may have dangerous voltage on it.
After reading this two decades ago, I was left with the impression that utilities in some areas actually were being required to install that five-wire system. Such as California. But I guess I was wrong.
Well I would respond that as far as ungrounded goes, that's how the grid started and there is still lots of delta distribution. Most of upstate NY is 4800 ungrounded Delta. I have never heard of any practical disadvantages of these systems, other than cost.Yeah and how do we know what all the problems would be with ungrounded or 5 wire until we build it? Just because we have small models of these systems doesn't mean it will scale up to the size of the North American power grid
Solid electrical connection
from the primary neutral to the secondary neutral. Such a
connection is unthinkable and unheard of in the industrial,
commercial and residential electrical engineering fields.
In Chicago in 1932, the transformers were failing. By this
time, the NEC was requiring grounding of the neutral in the
electric service to homes. The earthing connection was made
to the metallic water lines.
The Utilities Research Commission of Chicago and the
Engineering Experimental Station at the University of Purdue
conducted an investigation of surge protection of distribution
circuits as to why transformers were failing. Test involved the
interconnection of the primary lightning arrester ground and
the grounded neutral of the secondary main circuit.
The conclusions reached were, “Measurements of the
voltage between primary phase c lead and secondary neutral
have shown that the interconnection of the secondary
neutral with the lightning arrester ground is, in general,
beneficial to the transformer. In particular, with a low
resistance secondary neutral ground and a high resistance
lightning arrester ground, the interconnection reduced the
above voltage by 30 to 50 per cent.” [16]
Well I would respond that as far as ungrounded goes, that's how the grid started and there is still lots of delta distribution. Most of upstate NY is 4800 ungrounded Delta. I have never heard of any practical disadvantages of these systems, other than cost.
Certainly maybe. I wasn't using the fallacy "I haven't heard of a problem so there isn't a problem", I was just saying there is a lot of history with these systems so we should have good data on them.I always thought when you use deltas on a large scale you ended up with circulating currents do to the 3rd harmonic. I could be wrong, it was something I was told by a PECO engineer over 30 years ago