What's the best solution to protecting outlets with no ground , I was looking into it and what I found was the solution is to put a gfci, but would a gfci work without a ground ??
Because the source neutral is grounded. The circuit EGC has nothing to do with GFCI operation.
1 . How's is the source neutral grounded
2. would I have to put a gfci in each ungrounded outlet or will one protect the whole circuit
3. If not could I just put in a gfci breaker ?
By the utility and by the premises grounding-electrode system.
One will protect those fed from the load terminals.
Absolutely.
Back at the service and throughout the utility. Else why would you get a shock when you contact a hot and something connected to ground like a water pipe?
Either or.
You could.
-Hal
But in old homes with no ground there is still bounding ?
Honestly I wouldn't worry about it for most residential outlets as most general resi stuff doesn't have three prong plugs anyway.
I should have asked what kind of "protection" you're seeking.
An EGC assures that a L-G fault makes the OCPD behave like it would for a L-N fault.
So it will only protect the down stream right?
Absolutely again. It has to monitor the current in the circuit conductors.
In that sense, it's a "series" device (like a switch or fuse), not a "parallel" device (like a surge protector).
Not only downstream, but at the GFCI receptacle as well!
If there are any multi-wire branch circuits they will require GFCI breakers to be 2-pole with a load neutral output terminal.
After a MWBC splits into 2-wire branches you could use a GFCI receptacle and feed any more receptacles from its load side terminals.
Since your house is this old I don't think GFCI breakers is an option. If you can I would defiantly use these instead a receptacle GFCI. never know what was done in an old house and if your ever crawling under a house making sure the lines are GFCI is added protection.
Also tracing a GFCI is much better in a panel then behind a book shelf.
If this is a K&T installation and you use GFCI breakers, just be aware the neutrals might not be where you think they are, and there could be MWBCs that don't look like MWBCs.